Is a shower rcd, arranged ro the side of the ccu. What the correct procedure.

I'm earth on earth bar, neutral on bottom left on rcd, and live on top mcb. The rcd is just tripping once, says trip on the megger.

Should I do it inside the shower?
 
you should test the RCD at the RCD itself, with load disconnected
 
Is a shower rcd, arranged ro the side of the ccu. What the correct procedure.

I'm earth on earth bar, neutral on bottom left on rcd, and live on top mcb. The rcd is just tripping once, says trip on the megger.

Should I do it inside the shower?
You need to test the outgoing line and the outgoing neutral, with the earth on the earth bar.
The way you describe it, it would seem that you are testing the outgoing neutral and the incoming live. No wonder it trips.
What make of board is it?
Is this a split load board?
Maybe a pic would help...
 
You need to test the outgoing line and the outgoing neutral, with the earth on the earth bar.
The way you describe it, it would seem that you are testing the outgoing neutral and the incoming live. No wonder it trips.
What make of board is it?
Is this a split load board?
Maybe a pic would help...
That the board, do on the bottom neutral of the rcd and bottom of the mcb?
20210726_131853.jpg
 
Last edited by a moderator:
Well there’s a pointless shower isolator.

yes bottom neutral of rcd and bottom line, which is also bottom of mcb via busbar. Mcb off. Earth on earth

what tester are you using, and what setting?
It shouldnt trip at 1/2 x I
It should at x1 and x5
30mA setting?
 

Reply to Rcd testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
877
Given the RCD pictured below With the manufacturers instructions here: Am i right in interpreting that as well as being able to bring the...
Replies
4
Views
378

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock