Discuss Ring spurred at origin? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi all,

DIYer here. My garage has a double socket fed by 4mm2 twin and earth connected to the same circuit breaker has the ring main for the sockets upstairs in the house. The MCB is a B32.

Is the feed in the garage considered a spur from the ring main or is it a separate radial circuit which happens to be on the same MCB? Ideally I'd like to add more sockets to the circuit in the garage (using 4mm2) but is this safe or allowed?

Thanks.
 
It would be considered a spur and being 4.0 its method of installation would dictate whether it could carry 32A and be added to. Spurred points from ring final circuits are normally limited as to the number of points which can be served but the 4.0 clouds that a bit. It sounds like the garage socket has been a later addition and connected to the existing ring final circuit and if the existing circuit is wired using 2.5/2.5 conductors it is not ideal to have differing sizes at the same protective device, are there spare ways in your consumer unit.
 
If the 4mm2 is on the same circuit breaker as the RFC then it is a Spur, as for adding more sockets to the 4mm2you would need to swap the double socket for a Fused spur unit and add sockets from that spur unit, remember the extra sockets will be limited to 13Amps governed by the fuse in the spur unit.
Another method would be to take the 4mm2 to a seperate CB (providing there is one) and form a 32 Amp Radial to your Garage (assuming it's an atatched Garage), the proviso being is that your Garage would need RCD protection, if the garage is a standalone then a different set of rules apply.
 
The question as to whether this 4.0 can take 32A is down to its installation method. The spur is somewhat unconventional as it stands.
 
The question as to whether this 4.0 can take 32A is down to its installation method. The spur is somewhat unconventional as it stands.

The 4.0 is clipped along a roof joist in the garage, exposed to the air, no insulation etc. The consumer unit is actually in the garage, but there is no space for additional circuits.

We've only been in the house a few months so trying to understand what work has been done previously.
 
The 4.0 is clipped along a roof joist in the garage, exposed to the air, no insulation etc. The consumer unit is actually in the garage, but there is no space for additional circuits.

We've only been in the house a few months so trying to understand what work has been done previously.
Theoretically you could add to it but the best course is to connect to its own protective device but this is obviously not possible.
 
The spur is 4.0 clipped direct so in theory if he uses the same size of cable and installation method as the existing he could add direct to it. Personally I would like to see it on its own circuit.
 
Ideally I'd like to add more sockets to the circuit in the garage

What are you intending to plug into these sockets.
Is the 32A breaker protected by an RCD?
 
The spur is 4.0 clipped direct so in theory if he uses the same size of cable and installation method as the existing he could add direct to it. Personally I would like to see it on its own circuit.
A spur equates to One double or single socket
A One fused or unfused spur unit
A One fusedspur feeding a Fixed appliance.
The only way you can add more than one socket is on a 4mm2 32 or 30 Amp radial circuit if adding more than one the the cable used must be the same as the circuit is wired in 4mm2, this is the same for a 20Radial circuit wired in 2.5mm2
As the circuit in question is a Ring FC adding more than one unfused socket is not allowed
 
if the CU is in the garage anyway, why not split the tails with \Henley blocks and fit a "garage board". RCD + 2/3 MCBs. then a fault in the garage will not saffect the house CU andyou would have a spare way/s. a 4mm 32A radial for sockets, 6A MCB for lights.....
 
Thanks.

Based on what's been said, is the following an acceptable way forward?

>Replace the existing twin socket with a fused spur unit, fused at 13 amps.
>Add additional sockets from the fused spur unit fed by 2.5.
 
This is somewhat unconventional and is clearly ad hoc, yes it should be on its own circuit as I have also suggested but the limitations of what can be added to this spur is clouded by the cable size, 4.0. Appendix 15 which is informative does not demonstrate the use of 4.0 cables/conductors.
 
This is somewhat unconventional and is clearly ad hoc, yes it should be on its own circuit as I have also suggested but the limitations of what can be added to this spur is clouded by the cable size, 4.0. Appendix 15 which is informative does not demonstrate the use of 4.0 cables/conductors.
 
Thanks.

Based on what's been said, is the following an acceptable way forward?

>Replace the existing twin socket with a fused spur unit, fused at 13 amps.
>Add additional sockets from the fused spur unit fed by 2.5.

Yes .... And it's going to need to be tested
 
This is somewhat unconventional and is clearly ad hoc, yes it should be on its own circuit as I have also suggested but the limitations of what can be added to this spur is clouded by the cable size, 4.0. Appendix 15 which is informative does not demonstrate the use of 4.0 cables/conductors.
Yes it does on a 32 or 30Amp Radial circuit
Wired in 4mm2
2oAmp Radial wired in 2.5mm2
 
if the CU is in the garage anyway, why not split the tails with \Henley blocks and fit a "garage board". RCD + 2/3 MCBs. then a fault in the garage will not saffect the house CU andyou would have a spare way/s. a 4mm 32A radial for sockets, 6A MCB for lights.....

I assume that need to be notifiable under Part P?
 
Yes it does on a 32 or 30Amp Radial circuit
Wired in 4mm2
2oAmp Radial wired in 2.5mm2
I am talking ring final circuits. But yes you could consider this a 4.0 radial so I see no need for a fcu but circuit separation should be employed.
 
I assume that need to be notifiable under Part P?

Yes mate.

upload_2018-3-14_13-40-17.png
 
Thanks all.

Tempted to leave it as is for the time being and not add any additional sockets. There's a bathroom renovation on the cards soon where there is an electric shower running from a dedicated circuit. Once that has been decommissioned I'll ask he electrician to create a dedicated circuit for the garage sockets.
 
The more I read this thread the more confusing it becomes.

As far as I see it,

There is nothing wrong with a spur on a Rfc taken from the CU.
Its in the OSG 7.2.2 para 4.

The spur would normally be in 2.5mm2, but the fact that it's in 4mm2 is not a problem. (Might be a big garage, VD and all that)

If the socket is replaced with a FCU then there's no limit on how many sockets can be connected to the load side, as long as your happy with the 13 amp limitation.

As this is not a new circuit then it does not require Part P notification.
 
Is this because it's on a B32 MCB?
It's a spur from a 2.5mm2 RFC albeit from the CU, no problem with that, why 4.0mm2 was used is a mystery, it makes no difference to what you can and can't add, a spur is a spur, one twin or single socket only fed directly from the RFC without a FCU involved. Nothing to do with the B32 Amp CB rules is rules is rules.
 
Last edited:
As pete said, there isn't a rule, but there's nothing preventing it. Cable sizing in the guides are the "minimum " requirements.

We don't know the cable size in the RFC that the spur is connected to. The op has never declared that. The whole thing could be in 4mm2. It's pure speculation on our part that's its 2.5mm2 because that's the norm.
 
As pete said, there isn't a rule, but there's nothing preventing it. Cable sizing in the guides are the "minimum " requirements.

We don't know the cable size in the RFC that the spur is connected to. The op has never declared that. The whole thing could be in 4mm2. It's pure speculation on our part that's its 2.5mm2 because that's the norm.
And the fact that the OP has mentioned 4.0mm2 on several occasions, but yes the assumption is/was that it is a RFC wired in 2.5mm2 cable. Thanks for pointing that out.:D
 
The question as to whether this 4.0 can take 32A is down to its installation method. The spur is somewhat unconventional as it stands.
? sorry can you clarify
 
Just interested - how long is this 4mm spur cable?

Considering the 4mm is connected at one end at the CU (located in the garage) and to a socket at the other end (also located in the garage) I'm presuming it's not that long, unless the garage is massive and the route is silly.
 
Duel post, no idea why, apologies
 
Last edited:
Ah okay thanks for the reply, I did wonder, that explains your post :thumbsup:
It will be fine though
 
Is this because it's on a B32 MCB?
Considering the 4mm is connected at one end at the CU (located in the garage) and to a socket at the other end (also located in the garage) I'm presuming it's not that long, unless the garage is massive and the route is silly.

Perhaps its the same guy, who had the bathroom in his bedroom the other day; or was it a bedroom in his bathroom?
 
I wouldn't agree that the 4mm^2 part of the circuit needs to be considered as an unfused spur from the ring final circuit at all.

In my view it is clearly a hybrid ring/radial final circuit and in no way is it one of the standard circuits.

Assuming that the 4mm^2 cable is afforded overload protection by the 32A circuit breaker then it isn't unsafe to add sockets to the radial part of the hybrid circuit.

Presumably it was done because spare ways were not available or whatever. As I stated before my concern with the arrangement is solely the fact that there is unlikely to be an adequate connection/clamping of all the circuit conductors when they are of varying cross-sectional areas, and for this reason I would consider the arrangement to be wholly unsatisfactory.
 

Reply to Ring spurred at origin? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
785
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
Replies
3
Views
261
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
313
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
907

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock