Is a shed supply fed off a ring main via a 13a switched fuse spur allowed.
i was always taught it should be classed as a sub main And sub mains arnt allowed to be wired off ring mains
i recently done an EICR and come across this and coded it a C3
should I have coded it a 2?
 
Please don't take this he wrong way, but you last 2 threads have both been about EICRs, it seems you still have a lot to learn about doing them before doing anymore.

why would you code it?
 
I coded it cause I was taught that submains arnt allowed off ring mains
i haven't taken it the wrong way
I do a lot of testing and I always just write my queries down and pass them on to my superiors
but I really need to start asking more questions which is why I love this forum
 
It's good to ask and yes you will learn from doing it. You need to know and understand the regs to do EICRs, also a good knowledge of older versions too as you are assessing it to the current regs but it if complied to earlier editions then different codes may be needed.

What at was the sub main feeding? Was it a new DB or just sw fuse spurs and sockets?
 
So how is RCD/RCBO protection given to the sockets?
How is the cable run to the shed?
What OCPD protection is used for the cable feeding the shed?
 
The ring it's off is a true ring fed via a B32 MCB off a dual RCD board
The SWA is buried
everything is upto standard all bonds in place just this sub off a ring
 
The spur is part off the ring and the RCD is in the CU.
nuisance tripping was my only concern at first until my superior
informed me I should treat the shed as a sub main
 
IMO, it's not good practice, but from what you say, no regs. have been breached, so a code C3 would be my guess.
 
pretty good, hanging in the right place tonight :grin: this not being able to drink lark is getting annoying though, I am drier than the sahara and getting seriously cheesed off with it, the odd pint here and there is very frustrating lol
 
pretty good, hanging in the right place tonight :grin: this not being able to drink lark is getting annoying though, I am drier than the sahara and getting seriously cheesed off with it, the odd pint here and there is very frustrating lol

Mind over matter Mike, I am drinking a can of coca cola even though I have a fridge full of alcohol.
PMA as Delboy would say
 
pretty good, hanging in the right place tonight :grin: this not being able to drink lark is getting annoying though, I am drier than the sahara and getting seriously cheesed off with it, the odd pint here and there is very frustrating lol

Tell me about it!!

I haven't been allowed drink since October! :angry:
 
Is a shed supply fed off a ring main via a 13a switched fuse spur allowed.
i was always taught it should be classed as a sub main And sub mains arnt allowed to be wired off ring mains
i recently done an EICR and come across this and coded it a C3
should I have coded it a 2?

I thought a code 2 was only given for something that has a potential of being dangerous in the event of a fault. But I may be wrong.
 
Tell me about it!!

I haven't been allowed drink since October! :angry:
On a positive note I haven't been drinking the Creamflow you will be pleased to hear, I had a John smiths a week or so back but that was the first one in nearly 3 months lol, I hope you are feeling better fella, things will improve I am sure, fingers crossed for you anyhow.
 

Reply to Shed supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Im just curious as to peoples thoughts on the following install I seen on a video from an Electrical firm today and they did the following: Ran...
Replies
2
Views
551
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
509
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock