Patto
10.8 Kw shower on a 32A mcb keeps tripping in my girlfriends sisters newly purchased house, 10.8/230= 46.95A hence it tripping I would presume, also it's on a 45A pull cord and 6mm cable. I said it should be changed for a 50A pull cord and 10mm cable but her friend not an electrician said it's fine to just put a 50A mcb on the circuit as 6mm can take 50A no bother, I'm not a qualified spark but I am at college doing the best I can to become qualified, I see in the on site guide that reference method B says 38A for 6mm am I just being to "fussy" am I wrong that it should be 10mm cable also she is the kind of girl that's in the shower for 20-30 mins lol... genuine post this as I want to understand all options..
Thanks for any info given