Fresh back from a few days away, I'm tempted to ask "so would normal cable be flame propagating ? "
Fire rated cables I get, but is that the same as non flame propagating ?
May need to duck off back to Heidi Land :)
 
Think people are so blinded by Am 3 and fire resistant fixings they ignore the requirements for cable systems on escape routes and T&E most certainly would not comply even if it were fixed with indestructible clips. Comment frequently when doing FRAs on this type of thing.
 
Ok great, thanks for all your advice guys. And for those who were asking it was a grade D system
 
Try non fire propagating pvc conduit to bs en 61386-1
Bs en 50085
Bs 4607
All expectable in escape routes.

Winner rating??
Are we still in school??
 
  • Winner
  • Like
Reactions: 123 and bilbo_88
Reading that 422.2.1, towards the end it does say for BD2/3/4 the wiring systems shall be fire rated... (edit : just read Ian post #24 )
I did set fire to a cable to see what happened - not as bad as I'd hoped thought with the cable self extinguishing within about 10sec. Not surprising it failed IR testing after meeting Mr Rothenberger. Now for the pics :)

IMG_0637.JPG
 
Reading that 422.2.1, towards the end it does say for BD2/3/4 the cables shall be fire rated...
I did set fire to a cable to see what happened - not as bad as I'd hoped thought with the cable self extinguishing within about 10sec. Not surprising it failed IR testing after meeting Mr Rothenberger. Now for the pics :)

View attachment 36346
Try that with LSOH cable which is non fire propagating and will not give off the fumes standard twin & earth will
 
  • Like
Reactions: Wilko
Ok great, thanks for all your advice guys. And for those who were asking it was a grade D system
So what did the EICR say.
 
No - C3 maybe?
I would say it's more to do with a fire alarm service report issue and not a eicr.
You could note it on the eicr in comments if there was an issue but bs 7671 don't cover fire alarms.
Bs 5839 -1
Bs 5839-6 for dwellings
 
FP200 not used for smoke detectors- C2

Had no regulation reference or anything
I would contact them and ask their reasons. A Grade D system does not need fire resisting cable unless the requirements of BS7671 could only be met by doing so. I find it unlikely, though not impossible the reason is for an inappropriate wiring system on an escape route. More likely they have misread BS5839-6 or confused it with BS5839-1, the fact they have given a Code 2 is neither here nor there and it would be interesting to know why they have picked up on it to resolve your problem.
 
Reading that 422.2.1, towards the end it does say for BD2/3/4 the wiring systems shall be fire rated... (edit : just read Ian post #24 )
I did set fire to a cable to see what happened - not as bad as I'd hoped thought with the cable self extinguishing within about 10sec. Not surprising it failed IR testing after meeting Mr Rothenberger. Now for the pics :)

View attachment 36346

fire will tend to travel upwards rather than down so you have it biased towards self extinguishing there. If you did it again but set fire to the bottom of a vertical section of cable you might get it to burn a bit longer.
 
We are going off in a tangent here..lol
Domestic fire detection must meet BS5839 part 6 & BS 7671. Grade D can be wired from the consumer unit or from a local light fitting, in normal T&E. If specified then LSOH. As with emergency lighting, the units contain back up batteries. So the cable is sacrificial. The units also require a screwdriver to remove from the base, giving total isolation from mains, complying with the lockable isolation rule. Grading such as A,B,or C utilize a central psu, or control panel so the cable now becomes and issue to supply as long as possible. So here FP or Pyro would be required.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Smoke Detector Wiring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
34

Advert

Thread statistics

Created
bilbo_88,
Last reply from
tazz,
Replies
34
Views
7,539

Advert