Inspecting and testing a consumer unit as part of my training and have noticed that the circuit breaker for the SPD is on the RCD? I am unsure weather this is acceptable as I haven't come across this configuration and I am pretty new understanding SPDs could one of you more experienced people explain to me why it is or isn't it would really help with my understanding and training.


Untitled.png
 
No, it should not be off a 30mA RCD as it might trip it on a surge.

They are fine after a 'selective' RCD (once common as a TT incomer) as that will ignore short spikes of voltage leading to imbalance current (the sort of thing SPD deal with).
 
No, it should not be off a 30mA RCD as it might trip it on a surge.

They are fine after a 'selective' RCD (once common as a TT incomer) as that will ignore short spikes of voltage leading to imbalance current (the sort of thing SPD deal with).

I just asked one of the people I am training with and they said it was fine as this brand of SPD no earth leakage so can be installed downstream of an RCD/ RCBO. Would this then be fine if he is correct?
 
I hope you also noticed the missing busbar shield and unbalanced load between the two RCDs.

This is an image from screwfix site of that type of board, (BG) where the SPD is through an MCB, not an RCD. I can only assume your board has been retrofitted with an SPD, not original
IMG_3862.jpeg
 
Inspecting and testing a consumer unit as part of my training and have noticed that the circuit breaker for the SPD is on the RCD? I am unsure weather this is acceptable as I haven't come across this configuration and I am pretty new understanding SPDs could one of you more experienced people explain to me why it is or isn't it would really help with my understanding and training.


View attachment 108233
Surge protective devices (SPDs) should wherever possible be installed upstream of RCD to prevent unwanted tripping caused by transient overvoltages


Also 534.4.5.1
 
Last edited:
I just asked one of the people I am training with and they said it was fine as this brand of SPD no earth leakage so can be installed downstream of an RCD/ RCBO. Would this then be fine if he is correct?
The way an SPD works is by diverting the surge to earth. This will cause a trip leaving the surge free to find another route to earth.
Higher quality brands actually spell out that only a selective RCD may be fitted upstream, e.g. Schneider:

1684432477973.png

The BG spec sheet doesn't talk about coordination of devices, but does confirm my comment:

1684432449976.png
 
No, it should not be off a 30mA RCD as it might trip it on a surge.

They are fine after a 'selective' RCD (once common as a TT incomer) as that will ignore short spikes of voltage leading to imbalance current (the sort of thing SPD deal with).

This got me thinking; on a TT arrangement with an all RCBO board and no upfront RCD you'd need to provide a suitable RCD for the SPD?

What about boards whose SPDs don't require an MCB for protection presumably they would likely require a suitable RCD for fault protection if installed on a TT supply?
 
This got me thinking; on a TT arrangement with an all RCBO board and no upfront RCD you'd need to provide a suitable RCD for the SPD?

What about boards whose SPDs don't require an MCB for protection presumably they would likely require a suitable RCD for fault protection if installed on a TT supply?
I'm not following your reasoning. Why would you need to provide RCD protection for an SPD?
 
The SPD type for TT have one device L-N and another N-E to reduce the risk of a L-E short needing some means to clear it (e.g. an RCD up-front). Often they are used in most cases due to the 'safe' arrangement.

The SPD designed for TN systems have all devices from live-E but they don't have the same risk of L-E causing a live installation.

Personally, and due to being a bit paranoid (partly my nature, partly the Voice of Experience), I would use a 100mA selective RCD up-front of an all RCBO board just in case, but if properly installed and correct SPD used then it is not absolutely necessary.
 
In the regs they are refereed to as CT1 and CT2, but for a SP system they are often denoted as 2+0 and 1+0 (just to add confusion with Type 1 and Type 2 of course, as we have Type A and Type B RCDs along with B-curve MCB, etc.) or for 3P as 4+0 and 3+1, etc.

See Table 534.5 under regulation 534.4.6
 
In the regs they are refereed to as CT1 and CT2, but for a SP system they are often denoted as 2+0 and 1+0 (just to add confusion with Type 1 and Type 2 of course, as we have Type A and Type B RCDs along with B-curve MCB, etc.) or for 3P as 4+0 and 3+1, etc.

See Table 534.5 under regulation 534.4.6
You bring up an interesting point.
A Fusebox SPD kit has the L-N and N-E configuration and is advertised as suitable for TN and TT earthing systems. So I get quite used to not having to think too much about this topic. It's left me wondering whether any brands in the mid-range domestic market make different devices for TN and TT systems, mainly so I can store away the fact that I need to think if I deviate from Fusebox!
 
I think he is considering a L-E fault within the SPD itself not clearing the main supplier fuse.
My understanding is that the construction method makes this virtually impossible.

I'd be more concerned with ensuring the SPD was suitable for use with TT earthing, than considering an upstream RCD, although it seems that many now are.

Edit: above point covered in significant detail in subsequent posts.
 
You bring up an interesting point.
A Fusebox SPD kit has the L-N and N-E configuration and is advertised as suitable for TN and TT earthing systems. So I get quite used to not having to think too much about this topic. It's left me wondering whether any brands in the mid-range domestic market make different devices for TN and TT systems, mainly so I can store away the fact that I need to think if I deviate from Fusebox!
I think the argument for the 2+0 configuration for the TN-S case is under lighting surge conditions both L & N will both be disturbed by a similar amount w.r.t. E, so clamping both that way keeps the L-N difference down far more than the 1+1 configuration used for TT.

However, for the 1+1 configuration used for TT you get better clamping of L-N voltage for other sorts of disturbances such as fault-clearing or big motors being switched where the underlying surge voltage difference is between L & N anyway.

For TN-C-S is makes little difference given that N & E are tied together typically only a meter or so from the SPD
 

Reply to SPD on RCD acceptable or not? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I was looking at installing a SPD into an existing split load RCD BG consumer unit. In the instructions for the SPD it states that it may...
Replies
2
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K
My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
439

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock