Creamy Goodne5

Afternoon guys quick question

It’s been a year after the kitchen has been competed and now I’m looking at doing led strip lights under the cabinets on the plynths.

on one side of the kitchen I only have available 2 cooker isolating switches that I wired in for the induction hob and the electric cooker.

My plan is to spur off the outgoing of one of them in 6mm to a single socket immediately below them and plug the led lights it. They are 0.7 Amp zigbee lights.

is this ok? My only worry is an I correctly fusing the spur and would need an extra fused spur between the socket and the cooker switch. I can’t wire the led straight into a fused spur because it’s a molded plug with a transformer in it. I’ve added pictures for help
image.jpg
 
Not good design. I wouldn’t.
 
  • Agree
Reactions: Pete999
It's going to look a bit odd but you could replace one of those isolators with a cooker control unit. Does the circuit have rcd protection.
 
off 1 cooker outlet to 5A FCU then to socket as it's unlikely that the plug in PSU is fused
 
  • Agree
Reactions: pc1966
Getting 2 * 6mm in to one of the existing switches for a spur is going to be difficult.

If could put the new socket box adjacent to one of them so you could use a conduit coupler and two short bushes between them (so very little risk of cable damage) you could use a 1.5mm spur to a single 13A socket for the lights.

However going with the off side-mounted cooker outlet is going to be far easier and no additional box cutting and/or decorating to cover it up.
 
Are they reputable lights, or an eBay special?

@telectrix has a good point that they might not be very well protected from internal faults.
 
A socket-outlet could be connected to one of those circuits using 2.5mm² or as PC1966 says, even 1.5, although I personally would use 2.5 because it might be re-purposed later and there is more elbow-room with 2.5. The cable will be protected against overload by the nature of the socket, and against faults by the 32A MCB. All subject to the RCD of course.

I agree that some wall warts / adaptors that are not made to proper standards lack fusing, but that problem would be no different here versus plugged into the ring, plus a dodgy wall wart could be dodgy in other ways. So I wouldn't add an FCU to deal with that, I would bin it and get a proper one. It could possibly be replaced with and adaptor / PDE driver that has a mains cable rather than a plug, so that it could be wired into an FCU.
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Spur of a Cooker unit for under cabinet lighta
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Creamy Goodne5,
Last reply from
Lucien Nunes,
Replies
6
Views
3,803

Advert