May 7, 2012
117
24
93
I recall being taught that if you measure continuity between the MET and extraneous-conductive parts in a bathroom and, as a rule of thumb, it is either less than 1667 ohms or more than 1 M ohm, then you do not need supplementary equipotential bonding. I think I understand that the 1667 ohm figure comes from Reg 415.2.2 (R</ 50 VIa =50/0.03). Not really sure where the 1 M ohm figure comes from. Reading 415.2.2 though, I see that the 0.03 is if you have RCD protection. Well the bathroom does not have RCD protection yet (justifying a C3 I guess as it is compliant under older regs(or is it a C2)). Using the same formula R</ 50 VIa I now use App 3 to determine the current from a 6A BS60898 (MCB) to trip in 5s so Ia is 30A. So now we have 50/30=1.66 ohms. Testing between extraneous conductive parts in the bathroom and the MET I get greater than 1.66 ohms. So, according to 701.415.2 (vi) I need to apply supplementary equipotential bonding. Am I right so far?
Reading 415.2.2 it explains how to determine the effectivenessss of supplementary equipotential bonding but states that it is only required between simultaneously accessible exposed conductive parts and extraneous conductive parts. But I have only got a lighting circuit with a pull chord switch. So I have no simultaneously accessible exposed conductive parts and extraneous conductive parts, so I don't need supplementary equipotential bonding. Is that right?
I will add that I intend to fit an RCD but I'm just trying to understand the Regs.
I beleive that supplimentary bonding can be omitted now, as long as main equipotential bonding is in place with 30mA RCD protection.
And if anyone has already told you this in the time it takes to write this:
im a slower typer...
Thanks Jabbajaws. Happy with that but the bathroom has no RCD.
Can you maybe break this down easier to understand.
Why are you suggesting a required disconnection time of 5 seconds?
Is this an inspection only or are you carrying out work?
no, it's 230/30 = 7.667ohms.
you will have to upgrade the bonding, before carrying out any works!! also most on here will say rcd protection for the bathroom i say unless your putting a switch wire in the wall dont bother. tin hat on lol
It's my own house. I'm just trying to understand the Regs.
In order to determine the effectiveness of supplementary equipotential bonding 415.2.2 tells you to use the formula R</ 50 V/Ia (where Ia for an RCD is the tripping current (hence the 0.3 in the first calc (1667 ohms)). But if you have no RCD then 415.2.2 says Ia is the current causing automatic operation in 5 secs of the overcurrent device. From App 3, for a 6A BS60898 MCB this is 30A. So 50/30 = 1.66 ohms which I am exceeding. So I guess that means I need supplementary equipotential bonding. But if I only have a lighting circuit with a pull chord there is no simultaneously accessible exposed conductive parts and extraneous conductive parts and so there is no need for supplementary equipotential bonding. Are my assumptions correct?
as i said before. max. Zs is 230/In. so for a 6A 60898 type B that 7.67 ohms.
Touch voltage surely ?
However the upper limit is regarded as being 10mA maximum current flow from GN5 and GN8 for wet body conditions
which makes it
Rx > Uo /0.01 -1k ohms (body resistance 95% of population) = 22k ohms
measured in Zooilliamps :laugh:
Oh, me getting even more confused now, me thought that nominal voltage (230 in a domestic) was refered to as Uo for calcs in the regs. So whats the 50V ac bit mean then in 415.2.2? Also there are a lot of references to the magical figure of 1667 ohms on the forum which I thought came from 50/0.03 and the formula in 415.2.2?
which makes it
it's 2 different situations. max. Zs is to ensure disconnection of supply in the event of a fault of negligible impedance. supplementary bonding is to reduce the touch voltage between simultaneously touchable extraneous parts.
Reactions: 2 people
Thanks Tel. Thought I may be getting mixed up between different formula. And sorry about the overlap of replies earlier. I am happy with all the formula now and whichever one I use it points at the need for SEB (when there is no RCD); but if there are no simultaneously accessible exposed conductive parts within touching distance of extraneous conductive parts, I assume I don't need SEB. Is that right?
Yes, but the 3 conditions are required if Supp bonding is to be eliminated. from 701.415.2
1/ Disconnection time complying with 411.3.2.2 (this is your bit - max Zs)
2/ MPB in place to 411.3.1.2 (This is my bit - touch voltage)
3/ RCD to 415.1 (this provides compliance with 701.411.3.3)
If you have accessible extraneous conductive parts within a room containing a bath shower etc then you need supplementary bonding unless a RCD is fitted protecting all circuits and the 3 conditions that go with the RCD are met.
Tony - Thanks for the reply. So this is irrespective of the fact that I cannot simultaneosly touch exposed conductive parts and extraneous conductive parts? Only 2 extraneous conductive parts?
Looking at the post you must have access to the regs!
Have a look at sec 701 re loctions containing a bath shower etc re supplementary bonding!
Thanks Tony. So, to confirm. I need SEB even if I cannot simultaneously touch an exposed conductive part and an extraneous conductive part? In my situation I can only simultaneoulsy touch 2 extraneous condcutive parts.
Sorry about the duplicate thread. I have looked at 701. I just can't see the value in SEB if I can't touch exposed conductive parts.
it's more if you can touch 2 extraneous conductive parts. if 1 were to become live, due to a fault, then as long as the 2 were bonded together, there would be no p.d. between them , therefore no shock.
Oh Tel please don't tempt me over this!
OK. Bear with me. I am just tring to learn. So the lighting circuit in the bathroom is not relevant yeah? Because one of the the extraneous conductive parts could have become live due to a fault anywhere in the property? As I say bear with me.
not quite sure of your meaning, TC. you been on the fish heads again?
the point of bonding is to ensure that there;s no potential difference between extraneous conductive parts. imagine an earth fault ...... any bonded pipework will rise to 240V for the duration of the fault, till the MCB trips. as long as other pipework is bonded, it's potential will be the same. no PD = no current flow through you if you are in contact with both simultaneously.
If there is no RCD, then bond all pipework that enters the bathroom with 4mm cable. You can do this in an airing cupboard or loft, just so long as the pipework is continuous.
Come on chaps is relatively straight forward...
There are two conditions that exist in a location where you are naked and wet and hanging onto two metal bathroom components
1/ they are exposed
2/ they are extraneous
If they are exposed then they will be connected to the MET through the cpcs and 411.3.2.2 applies with 415.1
If they are extraneous then two further conditions are available:
1/ If they are connected to the MET via MPB and all metal pipework then 411.3.1.2 applies
2/ If they are isolated from the MET because of , either non metal pipework then GN5 and GN8 applies, that is
rx<= Uo/0.01 - 1k ohms which equates to 22k Ohms
So as long as simultaneously touchable metalwork is either bonded to MET or 'isolated' then you have some form of protection.
The confusion arises at what point does isolation stop and bonding begin.
Bonding to the MET infers that the touch voltage will not rise above 50V.
example: A lighting circuit protected by a 6A MCB has a maximum Zs of 7.67 Ohms which complies with table 41.3 but when compared with the requirements of 415.2 must not rise beyond 50V, so an alternative Zs tied down to the surrounding metalwork must be 50/Ia which would be 30A for a 6A MCB. This gives us a maximum Zs of 1.67 Ohms.
Now when used in conjunction with a 30mA RCD in compliance with 411.3.1.2, 415.2, 701.415.2
then Zs < Uo/IAN = 230/30mA
= 7.67 k ohms
This appears to comply with the disconnection time of < 40ms
However, even at 40ms (2cycles of ac) may still be sufficient to provide a kill
So to comply with touch voltage we have
Zs < 50/30mA = 1.67 k ohms
This satisfies both compliance for disconnection times 411.3.2.2 and compliance with 411.3.1.2
Now the problem arises when the resistance between simultaneously touchable parts sits somewhere between being bonded (> 1.67 kOhms) and Isolation (< 22k Ohms)
At this level both RCD and supplementary bonding needs to be present... cheaper just to supp. bond everything
Argue amongst yourselves
OK. Interesting stuff. But what is the answers to my question/s?
Yes I agree. An earth fault can give rise to PD between extraneous conductive parts. What is confusing me is 415.2.2 which explains how you determine the effectiveness of Supp Bonding between Extran parts and the calculation is based on Ia which is the current of the overcurrent protection device or the RCD in the bathroom. What has the circuit in the bathroom got to do with it when the earth fault could have been introduced to the extraneous conductive parts from any number of other circuits in the installation. Hyperthetically lets say there was no circuits in the bathroom at all; just a metal bath and a radiator with metal pipework. Some of the explanations above suggest that you could still get PD between the extraneous conductive parts and so it would be logical to apply Supp bonding. But how does 415.2.2 work in this case when for the formula is R</50 V/Ia there is no value for Ia.
If there is no potential difference between pipes that can be touched simultaneously,that is what is sought
All the regs and formulas only provide information to make a decision on what is necessary to obtain that situation
1/ they are exposed
= 7.67 k ohms
Yes - so from the red text above I need to add supp bonding if my Zs is exceeding 1.67ohms (no RCD). But if I can't touch anything on the lighting circuit simultaneously with extran parts why use Ia of the lighting circuit. If the earth fault was introduced, lets say by an immersion heater protected by a 40A MCB and no RCD. Ia would then be 200A (from Fig 3A4) and so your calculation would be 50/200 = 0.25ohms. In other words shouldn't we be using the largest value of Ia in the installation rather than the largest value of Ia in the room containing the bath or shower.
Yes I agree, If the lights or shaver sockets in the bathroom are class II or out of simultaneous reach. I was thinking along the lines of a snagged cable loose above the bathroom making fortuitous contact with the plumbing pipes as stuff gets moved about in loft spaces.
I chose a lighting circuit really to demonstrate that an earth fault voltage sitting on extraneous metalwork does not have to be 0.05 ohms, the largest Zs allowable which would keep the touch voltage to a maximum of 50V. If you had a 10.8kW instantaneous water heater which had caused an earth fault right above the cast iron bath you were standing in while having a shower then you would need a theoretical resistance path to the MET and around the bathroom to be no higher than 50/250 = 0.2 ohms. (personally I would prefer in this case the bath to be isolated from the MET and surrounding metalwork)
Now that RCDs exist and a global 0.4s disconnection time on final circuits, the importance of 'front line' protection by the use of supplementary bonding has lost its importance.
But we still have uncontrolled conditions out side of the installation such as network fluctuations in voltages, lost, damaged, or high resistance supply neutrals, which can lead to voltages appearing on simultaneously touchable metalwork for longer periods than 0.04, 0.4s, 5s. Voltages from PME systems could be there indefinitely until someone with wet hands and feet comes into contact.
Thanks for this reply and your previous one which was most informative. I now have a much better understanding. Maybe I have not articulated myself very well throughout this thread but it is 415.2.2 (using R</ 50 V/Ia to determine the effectiveness of SEB) that is causing me all the confusion. And which value of Ia to use. This and other forums suggest that you should be using the highest value for Ia that exists in the circuits actually in the room containing the bath or shower. I think that you should be using the highest value of Ia in the whole installation. Any thoughts on that interpretation?
The value of Ia will depend on the size of protective device used, that's precisely why 0.05 ohms is mentioned in GN3 as a rule of thumb. A coverall situation/application. I only use lighting as an example of one type of a circuit that will be in use while electric immersion,bath/towel/shower/convector/heaters are being removed for other forms of heating and is common to all bathrooms.
My interest is in knowing the limitations. We know the minimum desirable value of supp.bonding (< 0.01 ohm) But do we know what the maximum R would be or to see it the other way around, the minimum IR value to achieve an 'effective' isolation in the case of a fault or wayward external voltages affecting the potential on internal metalwork .
1/ they are exposed
= 7.67 k ohms
Looking for some kind of official source for meeting disconnection times/Zs and keeping touch voltage below 50v on both TN systems not just TT -Pre RCD or just without RCD with Fuses and MCB.
Maybe some old BS7671 or old Book, Workshheet etc? not sure I've got anything before 16th but if you point me in the right direction that would be great, Thanks
I've seen this and it's good but it does say
"Note that the touch voltage
may rise above 50 v; the
value of 50 v is used as a
constant in the formula to
ensure sufficient current is
flowing to operate the RCD."
so still a bit confused???
is 50v touch voltage really a thing?
Supplementary Equipotential Bonding
seftonbarn,
Mark Wright,