Hi folks,

I've recently visited a large 8 bedroom Victorian house. It has a three phase supply. One of the phases feeds the main house, its wired through a 100 amp main switch/ isolator. The Suppliers Side is 25mm tails but the customers side to the main house consumer unit appears to be 16mm. The run is around 20 metres or so and it looked like FP200 CABLE. Surely this should be 25mm going to the main house consumer unit?
 
Any chance of some pics of the set up.
 
Are you sure its not MICC cable, I'm sure they don't make FP cable in that size.
 
  • Agree
Reactions: Pete999
Are you sure its not MICC cable, I'm sure they don't make FP cable in that size.
Your probably right, I've not dealt with either. I was surprised to see it, I thought it was used for industrial installations.
Regardless of the cable type, would you not agree that it should be 25mm conductors for the L and N?
 
No. MICC has a much higher CCC than say SWA
 
  • Agree
Reactions: Des 56
No. MICC has a much higher CCC than say SWA
Okay thanks. Still not sure why it's been used in a house. I'm thinking about replacing it with 25mm SWA to the consumer unit and using pvc for the house circuits. Everything is done in MICC.
 
Why would you replace the MICC with inferior cables? Correctly installed MICC is a job for life
 
If you haven't dealt with it before,be wary of attempting to make any alterations that involve disturbing the terminations
 
  • Agree
Reactions: Strima
MICC is the best cable ever.
 
Hi,why not test it? Then you may be able to leave in,what will invariably be,the best choice of cable :)
 
Hi,why not test it? Then you may be able to leave in,what will invariably be,the best choice of cable :)

I'm going to test the whole installation but the consumer unit needs up dated and the customer would like additional sockets and lights etc. They said they wanted a rewire but testing the installation is probably the best option. I have no experience with MICC so now's the time to get it!!

View attachment IMAG0038.jpg

View attachment IMAG0037.jpg

View attachment IMAG0036.jpg

View attachment IMAG0035.jpg

View attachment IMAG0034.jpg

View attachment IMAG0033.jpg
 
Those protective devices are BS3871 type 3 for the orange ones and type 4 for the brown ones. The type 4 have never been recognised by BS7671 so you need to compare readings with manufacturers data, Federal Electric.
Take care working on them as they have a lot of exposed live parts. I see you are an apprentice so have you any testing experience.
 
Your probably right, I've not dealt with either. I was surprised to see it, I thought it was used for industrial installations.
Regardless of the cable type, would you not agree that it should be 25mm conductors for the L and N?

What do you mean regardless of cable type? Different types of cable have different current ratings.
MICC has a higher current rating than most plastic insulated cables for the same size conductors, 16mm is probably suitable for 100A, especially if you actually do the calculations rather than just using the tabulated values Uncorrected.
 
MICC is used in houses as I had it in my flat renovation, had to remove it as the CU was being located elsewhere and the if it was jointed then the run would have been longer then replacing the cable.

I loved PYRO back in the day, nothing more sexier then stripping 6 core Pyro in a hot sweaty basement with 6ft tails just in your boiler suit, sorry digressing a bit........... but the older members will remember....
 
You will need help from an experienced electrician, it’s not something you can just have a go at or make up as you go along.
Thanks I'm aware of that, I'm doing my research and getting advice from older, more experienced colleagues before I make any decisions.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Advert

Thread statistics

Created
James Neilson,
Last reply from
James Neilson,
Replies
19
Views
2,772

Advert