Evening all,
Can you give me some advice. I have been to do some testing today at a premises that is on a farm which has a 3phase +Neutral incoming supply. as a TT system. there are no signs of any earthing arangments what so ever.
the part of the system I have been to look at is fed via on of the phases plus the neutral thru a 63amp fused isolator. out of the isolator there are 2 feeds each going to its own CU in diferent areas again there are no signs of any earthing at either of the CU's.
question 1, because there is no earthing arangment I cannot take a Ze reading, ( obviously as theres no earth). would this also not mean then that the Zs reading for each cct is unobtainable too?
question 2, whilst testing for the pfc between phaseL and phaseN at one of the CU's at the main isolator with it in the of position I get a reading of 70A, would this be a true reading or is it likely to be being affected by the suplly to the other CU? would I need to disconect one of the CU's at the fused isolator to make them "individual" ccts?
Question 3, to rectify the fault of the earthing, I would propose to put an earth spike/electrode in the cct, 1 for each CU and then change the CU for the correct type for a TT system, (it is not right at the minute) what are your thoughts on this as opposed to using on spike for the "whole system at the incoming source. trouble is I dont really want to get involved with the "rest of the system as it has dis boards and feeds going all over the farm to various units etc.
thanks for any help, appreciate it. Ross
Can you give me some advice. I have been to do some testing today at a premises that is on a farm which has a 3phase +Neutral incoming supply. as a TT system. there are no signs of any earthing arangments what so ever.
the part of the system I have been to look at is fed via on of the phases plus the neutral thru a 63amp fused isolator. out of the isolator there are 2 feeds each going to its own CU in diferent areas again there are no signs of any earthing at either of the CU's.
question 1, because there is no earthing arangment I cannot take a Ze reading, ( obviously as theres no earth). would this also not mean then that the Zs reading for each cct is unobtainable too?
question 2, whilst testing for the pfc between phaseL and phaseN at one of the CU's at the main isolator with it in the of position I get a reading of 70A, would this be a true reading or is it likely to be being affected by the suplly to the other CU? would I need to disconect one of the CU's at the fused isolator to make them "individual" ccts?
Question 3, to rectify the fault of the earthing, I would propose to put an earth spike/electrode in the cct, 1 for each CU and then change the CU for the correct type for a TT system, (it is not right at the minute) what are your thoughts on this as opposed to using on spike for the "whole system at the incoming source. trouble is I dont really want to get involved with the "rest of the system as it has dis boards and feeds going all over the farm to various units etc.
thanks for any help, appreciate it. Ross