Another disparaging Hager-related question: does anyone know if it matters which set of terminals are feed power, and which are load for RCDs?

Typically incomer RCDs are fed from the bottom, but the supplied instructions/datasheet (for what they are worth) for the likes of the CDA425U 4-pole RCCB do not indicate any preferred direction for power (i.e. power supplied from below on even-numbered terminals, or from above on odd-numbered terminals). One side obviously must power the electronics, but it may or may not matter is that remains live upon a trip event.

I asked Hager technical support and they sent me the data sheet, so obviously did not read my question as I had already referred to it :(

So I asked again and no reply for 2 weeks now.

Any thoughts?
[automerge]1592810112[/automerge]
Amazing, just on posting this I got a reply:

"Our Main switches & RCD are neither pole dependant and makes no difference if you feed the supply from the top nor bottom."

So now this post is just for general interest.
 
I know it doesn’t matter regarding in and out but reply from Hagar? ‘HAGAR IS WATCHING’ ??? and on the ball, too. (today)
 
Sorry probably a bit dense of me RCD in ccu would be fed from the top yours is some kind of FCU RCD ?

Side not I've sent Wylex message requesting info on a RCBO trip curves etc that I can't find anywhere what are the chances Ill get a reply like you got from hager
 
Sorry probably a bit dense of me RCD in ccu would be fed from the top yours is some kind of FCU RCD ?
In a "type B" TPN board the power comes up to the central bus-bar arrangement from below.

But in our case we have some separate RCDs in a DIN rail box as you can't so easily (or cheaply) get RCBOs for 3-phase, or double-pole RCBOs for single phase, for most UK TPN boards. Also we have a few other oddities to connect so the DIN box is handy.

Side not I've sent Wylex message requesting info on a RCBO trip curves etc that I can't find anywhere what are the chances Ill get a reply like you got from hager
Don't hold your breath!

I'm still waiting for clarification of the Wylex industrial MCB current limits, but gave up and moved to Hager (for other reasons, not simply the lack of an answer).
 
I always wondered how you add a RCD to a TPN board with bus-bar down the middle going to the MCBs , assumed it must go where the isolation switch is or you HAD to use RCBOs
Some of the manufacturers offer RCD add-ons that basically flip the MCB leaver to do implement an RCBO arrangement but, AFIK, only Schneider offers a neutral bar option for this sort of thing to be neat/simple and even then it is still not so neat as a proper RCBO the RCD is taking at least another 3-way slot out of the TPN board.

It is fairly common to have an RCD incomer on TPN boards, but usually for TT supplies (or for fire risk reduction) as a 100mA / 300mA delay type.
 
Getting DP RCBOs is not too hard, making them fit their TPN board is the real challenge...

You see a lot of DP RCBO in use for the likes of caravan feeds, etc.
 

Reply to Top-feed or bottom-feed RCDs? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
727
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
296
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
751

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock