I don't like the idea of a device which deliberately creates a fault in order to trip an RCD, if the RCD doesn't trip then it's just creating another fire risk. It would be better to operate the RCD via a shunt trip or undervoltage release in my opinion.

Also I'm not entirely convinced that switching off the power after a fire has started and set the smoke alarms off is going to be quite as helpful in stopping fires as is suggested.
 
  • Agree
Reactions: Wilko
I'm not either you could be creating further danger by tripping out lights on dual RCD consumer units, may be ok if works with several RCBO's that supplies curtain circuits.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Midwest

Arms
Supporter
~
Joined
Location
Oxfordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Title
TripActivator | RCD Fire Safety
Prefix
N/A
Forum
Electrical Tools and Products
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
Midwest,
Last reply from
Toneyz,
Replies
2
Views
1,276

Advert