Hi al,
Just need a bit of a refresh regarding the sizing of the earth cable for a domestic installation with an earth spike. I believe 10mm for the gas & water bonding, but seem to recall that the main earth cable can also be 10mm?
On a TT system the earth cable to the spike can be 6mm, but I always fit 10mm as it makes sense when your equipotential bonding is 10mm
As others have said, it doesn't have to be 10mm, and can be 6mm, but as I usually carry 10mm for main bonding anyway, I usually use this, as it saves having to stock/carry another roll/size of cable
I would size it according to pme supplies, not that it needs it at present.
Two reasons
1/ Possible upgrade at a future date to pme
2/ Mechanical protection of the the earthing conductor and from corrosion.
TT main earth 2.5mm² minimum, if mechanicaly protected, 4mm² if not (Reg. No. 543.1.1).
If buried, 16mm² sheathed, 25mm² unsheathed (table 54.1).
Bonding 6mm² minimum (Reg. No. 544.1.1).
Originally Posted by Sickmick
Main bonding hasn't got to be 10mm on a TT system.
Can you point this out in the regs please as my copy seems to have omitted this!!!
For a TT system you can have a 2.5mm main protective conductor if you so wish and the way to size is is done via reg 543.1.3.
Not really sure what you are getting at Malcom ???
Ahhhhhhhhhhhhhhhhhhhhhhhhh Trip to spec savers for me
Sickmick I do apologize I missed the 't from you post, but it is an age thing
And spark 68 thanks for pointing that out, before I crashed into a heap.
:leaving:
so that's me leaving
couple of large shots of JD might help, malc.
Reply to TT Earth cable sizing in the Australia area at ElectriciansForums.net
Hi all, just a quick one on an earthing arrangement for a radial circuit on a wooden workshop I have just had installed. I have run a 3 core 2.5mm...
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Hi, thanks for reading this. Ive been asked to look at a job where the DNO connection (single phase 80A TT) is a long run to the final circuits...