Hi al,
Just need a bit of a refresh regarding the sizing of the earth cable for a domestic installation with an earth spike. I believe 10mm for the gas & water bonding, but seem to recall that the main earth cable can also be 10mm?
 
On a TT system the earth cable to the spike can be 6mm, but I always fit 10mm as it makes sense when your equipotential bonding is 10mm
 
As others have said, it doesn't have to be 10mm, and can be 6mm, but as I usually carry 10mm for main bonding anyway, I usually use this, as it saves having to stock/carry another roll/size of cable
 
I would size it according to pme supplies, not that it needs it at present.
Two reasons
1/ Possible upgrade at a future date to pme
2/ Mechanical protection of the the earthing conductor and from corrosion.
 
TT main earth 2.5mm² minimum, if mechanicaly protected, 4mm² if not (Reg. No. 543.1.1).
If buried, 16mm² sheathed, 25mm² unsheathed (table 54.1).
Bonding 6mm² minimum (Reg. No. 544.1.1).
 
quote_icon.png
Originally Posted by Sickmick
Main bonding hasn't got to be 10mm on a TT system.
Can you point this out in the regs please as my copy seems to have omitted this!!!

For a TT system you can have a 2.5mm main protective conductor if you so wish and the way to size is is done via reg 543.1.3.

Not really sure what you are getting at Malcom ???
 
Ahhhhhhhhhhhhhhhhhhhhhhhhh Trip to spec savers for me

Sickmick I do apologize I missed the 't from you post, but it is an age thing

And spark 68 thanks for pointing that out, before I crashed into a heap.

:leaving:
so that's me leaving
 
couple of large shots of JD might help, malc.
 

Reply to TT Earth cable sizing in the Australia area at ElectriciansForums.net

Similar Threads

Hi, thanks for reading this. Ive been asked to look at a job where the DNO connection (single phase 80A TT) is a long run to the final circuits...
Replies
4
Views
281
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
631
Hi I have a domestic installation to rewire and the main incoming fuse is 80 amp so i am using 16mm double insulated tails, is the main earth size...
Replies
6
Views
2K
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
I have had these lights installed by a contractor whose work is normally very good. He has not connected the earth in each fitting as there is a...
Replies
37
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock