Hi I have a domestic installation to rewire and the main incoming fuse is 80 amp so i am using 16mm double insulated tails, is the main earth size with this 16mm or 10mm ? Thanks
If you are referring to the typical UK insulated and sheathed singles used as meter tails these don't include a protective conductor in the cable. The norm would be to run a 16mm^2 Earthing conductor alongside.
 
If you are referring to the typical UK insulated and sheathed singles used as meter tails these don't include a protective conductor in the cable. The norm would be to run a 16mm^2 Earthing conductor alongside.
ye if it was a 100 amp main fuse i would install 25mm double insulated tails with a 16mm earth, so if it is an 80 amp fuse then i know i can use 16mm double insulated tails but is a 10mm earth sufficient or does it have to be a 16mm?
 
ye if it was a 100 amp main fuse i would install 25mm double insulated tails with a 16mm earth, so if it is an 80 amp fuse then i know i can use 16mm double insulated tails but is a 10mm earth sufficient or does it have to be a 16mm?
If selected (as opposed to calculated) then 16mm^2 is required. As I stated, 16mm^2 is the norm.
 
so cpc being minimum of half the live conductor size does not apply here then?

No, see table 54.7 in the regulations for the full story.

If you are using the table 54.7 method of selecting a protective conductor size then for a line conductor of 16mm,25mm or 35mm the protective conductor needs to be 16mm.
 
ye if it was a 100 amp main fuse i would install 25mm double insulated tails with a 16mm earth, so if it is an 80 amp fuse then i know i can use 16mm double insulated tails but is a 10mm earth sufficient or does it have to be a 16mm?

This depends on a number of factors.

If you are using the table 54.7 method then it will need to be 16mm.

If, however, you are calculating the size required then you may find that 6mm (or less) satisfies the adiabatic equation. But you also need to consider the earthing system as this will affect the size that the earthing conductor needs to be to satisfy bonding requirements.
 

Reply to size of earth on 16mm mains tails in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Replies
5
Views
957
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
728
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
399
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
678
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
807

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock