Hello,

I've been asked to install a supply for a TP air source heat pump to heat a swimming pool.

The pool room CU is feed from a barn with a TP supply and luckily the SWA feeding the pool room CU is a 4 core.

The barn is going to be converted in the near future into 2 holiday lets so I'm going to upgrade the ancient board that's in there.

My question is can I cover the couple of SWA submains by a 30 or 100ma time delayed RCD and have it conform? I have hardly touched any TT systems as we don't have many around where I am.

Many Thanks.
 
Time delayed 100ma S type are usually a main switch with a split load board of maybe 2 30 ma RCDs to give you discrimination. What is the type of supply at the origin. Is the ground condition suitable to drive in a Earth Electrode, may be test the soil resistance first if you can The issue I think you may have is the inrush currents of the heat pump unless it has a soft start built in. Rcd’s don’t usually like high start up currents. The heat source pump Would need to be protected by a 30 mA Rcd .
There is bound to be other guys replying once the pubs turn out .
 
Last edited:
At the source I have a 3 phase TT incomer supplying a 3 phase board. There's 3 sub mains from that board to the pool house, tennis court and garden room.

My plan is to upgrade the 3 phase board in the barn using a 4 pole 100ma time delayed RCD as the main switch to cover the 2 SWA sub mains and then 30ma RCBO the barn finals. Then have a 1 way three phase board in the pool house for the pump.
 
At the source I have a 3 phase TT incomer supplying a 3 phase board. There's 3 sub mains from that board to the pool house, tennis court and garden room.

My plan is to upgrade the 3 phase board in the barn using a 4 pole 100ma time delayed RCD as the main switch to cover the 2 SWA sub mains and then 30ma RCBO the barn finals. Then have a 1 way three phase board in the pool house for the pump.
Your Plan sounds okay to me as long as you get a low enough Earth Electrode resistance. I think you may need to check with the Pump Manufacturer as to what 3-phase RCBO or RCD they may specify. C type etc. They will know the expected inrush current.
 
Both 100mA and 30mA RCDs should have rod impedances less than 200 ohms (for evidence of stability of earthing, not the 500ohm/1.67k that 50V/In gives) and that is normally OK to meet with a single rod.

But check any existing rods for both soundness of connections and their Ra.
 

Reply to TT Submains time delayed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
869
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
624
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock