R
radiohead
Not a good idea to use single pole devices, either mcb's or SP RCBO's on a TT with an upstream T/D RCD. A fault which trips a SP device on a final circuit will not disconnect the neutral on that circuit, the upstream RCD will possibly still trip disconnecting the entire installation because a N-E fault may remain in place.There is another minor advantage to an up-front RCD as normally it would be 100mA delay (S-type) to discriminate against down-stream 30mA RCD tripping, and that would allow using only a MCB for fixed things like immersion heaters or cookers (those without 13A socket feed) that are prone to nuisance tripping 30mA devices due to normal non-trivial leakage currents
In practice DP RCBO's are the only way to achieve compliance on a TT if an upstream RCD protects the DB.