This is a proper earth pit:
View attachment 20152
It is important to note that this isn't the usual chang wang piece of excrement peddled by some electrical wholesalers which is essentially a cheap plastic box with a sticker on it like the one you describe. For a TT system where you want to achieve TN Ra values, unfortunately the 3/8" 4ft rod just won't cut it I'm afraid (I'm not bad mouthing the 3/8" rod [or the twig as it is often described], I'm purely stating that it isn't suitable for this task). You would need to use a 5/8" rod, some are sold at lengths of 12ft but more likely you will find them 4 ft in length but with the ability to couple to other 5/8" rods by using an earth rod coupler. This way you can achieve great depth and very stable results.
This is how I would star link more than one rod (apologies for the rather rudimentary drawing):
View attachment 20153
I must note that there are many more methods available when it comes to linking rods together however in many cases the method used to link them together is often down to personal preference and often down to common sense. I prefer this method over just linking from one to the next in case the link between the first rod and the MET gets broken somehow leaving the installation unearthed! It also keeps the resistance of the main earthing conductors low as it uses four shorter lengths instead of one long linked length.
If a main earthing conductor is not mechanically protected then it should be buried at a depth of at least 600mm and must comply with 542.3.1, in particular it must be sized in accordance with table 54.1.
The key to achieving effective earthing in a star linked configuration is to ensure that the distance between each seperate rod is at least ten times the length of the longest rod so as to prevent any rod from intefering with another's zone of influence. For example, if you have used four linked 4ft rods (a total of 16ft depth) then the distance between that and any other rod should be at least 50m.
Hope this helps explain things a bit better.
That Is really good and clear
thanks for the info As you state I have only come across the twig rods this was all that was supplied when I was training and carrying out domestic rewires
I can rember learning about earth rods at college and that they have to be installed at a distance of ten times the length of the rod to make sure that the zones don't interfere with each other
With regards to the earth pit I take it you dig a hole to sink the cover so it's level with the ground and then install the rod into this.
I also guess the reason for the pit is to provide a means to inspect the rod and connection when carrying out inspection and testing in the future
Thanks for the diagram of star linking rods it makes it clearer
I can see why it's better to run seperate cables to each rod rather than link all 4 with one cable
Can I just ask would you just install the cables direct in the ground at greater than 600mm or do you install mechanical protection using galv conduit or ducting ?
Thanks for the info and taking the time to share your wisdom it's really useful and good to know for future should I have to install a TT system
I won't be installing any more twigs