Gavin John Hyde

-
Esteemed
Arms
Patron
Reaction score
5,173
At a house today fitting yet another car charger.
Straightforward install apart from fuse holder having a crack in it.
Called SSEN who sent an engineer out, he pulled fuse and replaced holder.
Install was overhead TT to old cottage. live fused neutral comes in via a henley block before going through meter.
I had an Ra of 86 Mohms so reasonably happy given ground conditions
We got talking about things as you do he then said I will convert it to PME for you if you want,
Okay,, expecting him to change cut out etc. he then runs a piece of 16mm earth from MET to the Neutral terminal/henley block!
Just like that, I asked him about what he just did and he said all the cables outside are basically PME now and its no problem.
Weird thing is if i had requested PME SSEN would have wanted ~£200 for it.
Anybody else had DNO just connect Neutral and Earth together and say here's your PME?
I recognize a lot of the cables out there before entering the house are PME'd and very little is still TNS.
I thought they might want to carry out checks further along the supply before doing it.
That said have seen plenty of DIY PME conversions when out and about. can never be sure if it was a dno job or DIY job...
A part of me thinks this is all good and well until one of them gets it wrong.

On the positive side now have a Ze of 0.19!
 
I'm impressed to see an overhead feed to a cottage being as low a Ze as 0.19 ohms!
So was I - that why i figured it was still TT and hadnt been converted until now..

As rural as it is, I expect there has been a lot of work to the network. Funny thing is the houses down the road - around 100m are PME with proper PME heads. they were converted from old barns/stables with new supplies around 2 years ago.
 
If installing a car charger would it not have been easier to keep it TT, and then not have to worry about PEN fault protection, etc etc

I guess getting it converted to PME means you dont need to worry about the possibility of the TT system being connected to the PME earth via water pipes and the like to the other houses, although if those houses are new conversion probably plastic pipe
 
If installing a car charger would it not have been easier to keep it TT, and then not have to worry about PEN fault protection, etc etc

I guess getting it converted to PME means you dont need to worry about the possibility of the TT system being connected to the PME earth via water pipes and the like to the other houses, although if those houses are new conversion probably plastic pipe
Charger can use PME as per Manufacturers specs. With exception of Ohme chargers I only fit ones that can use PME now. makes life so much easier.
 
SSE are really good. I've had them swap to PME a few times with no charge. I think all they do is quick Ze check to see if suitable. You have to make sure bonding is upgraded to 10mm which could add to the work.
 
IMG-20210608-WA0000.jpeg
boys fitting these yokes today.. just swipe the card it seems....
 

Reply to TT to PME conversion in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
535
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
696
Hi guys, Had an issue at a recent survey where doing a quick check and found we had pme with a reading of 0.44 ohms. Called the network and they...
Replies
5
Views
365
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock