Hi all, we are currently carrying out PIR's on resisdental properties/flats, but only the common areas,landlord supplies.My problem is that today i came across a landlords supply which share its supply with lots of flats and for various reasons i was unable to turn off supply, disconnect main earth and carry out Ze test. So my question is: for page three(main characteristics) do i just write lim down for Ze and PFC or maximum values? i.e for TNC-S 0.35ohms unsure of max PFC? kind regards simon
 
Enquiry is another option, by ringing the energy provider and asking them! PFC should be tested live so ......
 
PFC can still be measured as the main bonds and earth are connected for this test. As for the Ze on a PIR that i could not isolate i would test with earth connected and note on cert that Zdb has been taken as Ze.
 
okay no problem will take the measurement from landlords db as i cant pull main fuse to test pfc as im aware the main bonding/earth should be left connected due to parallel paths/worst case.
 
PIR certs have a very useful limitations section on the front page.
As long as you can reasonably justify your limitations, i.e. 'unable to test for Ze as not safe to remove main earth', then just put LIM in relevant box.

I often find that when I carry out a PIR in an occupied unit/property you just cant go disconnecting supplies, or isolate server circuits, or remove sensitive equipment to enable an IR test. there's always something stopping you carrying out all the tests, so you just go for a LIM and justify it. just don't take the ****!
 
Last edited by a moderator:
okay no problem will take the measurement from landlords db as i cant pull main fuse to test pfc as im aware the main bonding/earth should be left connected due to parallel paths/worst case.

Yes, I'd prefer to see a value in the Ze box and an explanation that the value was measured with all bonding etc. in place due to resident constraints.

Why would you 'pull the main fuse' to do PFC?
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
unable to measure Ze!
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Thread Tags

Advert

Thread statistics

Created
mini-si,
Last reply from
IQ Electrical,
Replies
5
Views
4,780

Advert