Hi,

I`ve been to a site today and noticed some units I`ve got have huge voltage drops. Voltage was fluctuating between 170V and 280V and on some units, I`ve had 330V.
I went to the DB board:
  • Between live and earth some circuits were showing 217V and other one were showing 270V.
  • Between Neutral and Earth, some circuits were showing 60V. When isolating each all MCBs, I`ve had 240v between neutral and Earth.
  • The main supply was ok.

It looks like the issues is on the floor and feedback this on the DB board.

There are about 15 circuits. Each of them is connected to two spurs and feeding some VAVs boxes.

What could be the reason of the voltage fluctuating like this?

Many thanks,
 
As James, it's a Neutral issue, poor or dis connection, either at the 3 phase DB or at the source to that D.B
 
Last edited:
Yes, it needs to be resolved as some of the transformers burnt and we had some fire in some boxes.

Can the issue with the neutral comes from the floor of the DB board itself? I mean can the neutral disconnected be found on one of the spurs?
 
I mean can the neutral disconnected be found on one of the spurs?

No. It will be on the 3-phase supply before the first point at which abnormal voltages are found.
 
If the O.P was only onsite for HVAC then I suggest the voltage issue is reported to whoever is responsible for electrical distribution within what's left of the building, URGENTLY.
Corrected that for you.
some of the transformers burnt and we had some fire in some boxes.
You make it sound like this is a normal everyday type of problem!

Turn the power off!
 
Not quite understanding why you would spend time identifying voltage issues and then ................
Post on a forum to ask for a reason as to why the voltage was fluctuating

It brings to mind Nero fiddling while Rome burned
 
Agreed with the above - if you find a situation like that, you report it to the responsible person immediately. It's not a "get a brew and write a letter" sort of immediate, it's a find them in person or pick up the phone immediate. The mention of "some of the transformers burnt and we had some fire in some boxes" should be enough of a clue that it's both serious and urgent - threat of fire and threat to life serious.
 

Reply to Voltage Fluctuating between 170V and 330V in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
527
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
661
Hi all, any advice would be greatly appreciated. Went to do some work at a factory unit on Monday ( changed 20 florries to LED battens and changed...
Replies
3
Views
649
I am having a weird issue at my home that has been getting progressively worse over the past few months. It all started out with some specific...
Replies
5
Views
1K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
771

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top