BrianHJR

DIY
Reaction score
15
If sleeving conductors at both ends, does it really matter which underlying conductor colour is being used for what?

Background is that I’m installing an electric boiler into a commercial building for a charity. The boiler is single phase, 12KW, 63 amps rated with 10mm conductors specified.
The DB is 3 phase.
The new installation will be professionally tested by a qualified professional as soon as possible after installation.

Due to having been donated a roll of 3x16mm SWA, that’s what I’m using from the 63 amp MCB in the DB to a rotary switch coupled to the boiler, with 10mm singles from switch into boiler terminals (because 16mm will not fit the screw terminals).

The 3-core is in new tri-phase colours. Therefore I’m questioning which I should best use for this single phase supply.

As I understand it’s preferred to dissociate the black colour from the old use as a neutral, I’d had that set aside as the earth conductor and sleeved accordingly.
That leaves me with grey and brown for phase and neutral.
Boiler is going to be running off the grey phase, but I understand the live will need to be sleeved in brown anyway? So what is likely to cause the least confusion?
Grey sleeved in brown as phase, and brown sleeved in blue as neutral?
or brown unsleeved as phase and grey sleeved blue as neutral? This is certainly simpler.

Am I just overthinking all this as the sleeving makes the original colours irrelevant anyway?
?
Thanks in advance...
 
It doesn't really matter providing they are correctly identified. A single phase line conductor should be brown so it makes sense to utilise the brown. Most people use the grey as neutral and black as cpc but as already stated it doesn't matter providing they are correctly identified. Have you ever made off a 16.0 swa before especially at a rotary switch, that will not be easy.
 
Thanks for the confirmation.
I did some 25mm on the main installation - it’s getting more like plumbing than wiring at that size...
16 doesn’t seem too bad in comparison. But yes although tight, it’s a big TPN switch so there is room to manoeuvre...
 
A further question; the installation manual stipulates heat resistant cable for the final connection into the top of the boiler where the main power connects into terminals on a circuit board, very close to the exiting copper flow pipe.

I can procure 10mm heat resistant flex, albeit at exorbitant cost to the charity for a single meter (we only need less than a foot)!

The terminals inside the boiler appear suitable for this specification of stranded type cable, but those inside the rotary switch will likely not - will I need 10mm ferrules?

If I use standard PVC cable singles could it be fitted with a heat resistant over-sheathing instead?

Thanks again. I work full time and volunteer my occasional spare days to do this work for the charity, so I have to try to use time and resources as efficiently as possible...
?
 
If they are not clamp type terminals then yes you should fit ferrules for flexible cable.
 
You can ask the electrician who is signing it off if they have the tools and parts otherwise you are stuck unless you purchase the tool.
 
You can ask the electrician who is signing it off if they have the tools and parts otherwise you are stuck unless you purchase the tool.

I can’t guarantee their availability and we can’t afford too much of their time, so I’d prefer to get it sorted ASAP and then just have them turn up with it ready to go.
I’m leaning towards standard singles and heat resistant sleeving as that’s looking like the lowest cost and quickest option...
 
If the instructions recommend heat resistant cable then that is what you should use.
 
  • Like
Reactions: DPG
The manual also states that the installation should be done in accordance with the relevant regulations.
Does anyone have sight of the part of them that covers heat resistance?
I would be inclined to put forward the hypothesis that standard cable becomes heat resistant cable when appropriately sleeved, but I’d be interested in any other opinion.
 
Relevant Regulations could cover a multitude of different things which is why it is a minefield for someone who isn't suitably equipped/competent to do this sort of thing. Charity or not it is always advisable to seek a professional to carry out these works.
 
Relevant Regulations could cover a multitude of different things which is why it is a minefield for someone who isn't suitably equipped/competent to do this sort of thing. Charity or not it is always advisable to seek a professional to carry out these works.

Thanks for your concern.
That’s not going to happen, although as I say the installation is being completed to a sufficiently high standard to ensure that it can be tested and inspected as safe, by a suitably qualified person.
 
Thanks for your concern.
That’s not going to happen, although as I say the installation is being completed to a sufficiently high standard to ensure that it can be tested and inspected as safe, by a suitably qualified person.

You will need to ask whoever is testing and certifying it if they are willing to put their name to normal pvc cable with heatproof sleeving.
 
If there is a circuit board inside the box it's unlikely to be getting particularly hot, although the heat developed in the connection resistance and the normal dissipation of the cable will raise the temperature of an already warm cable. Heat-resistant sleeving will not stop the original insulation deteriorating at high temperature. What can ultimately happen in extreme cases is that the insulation hardens and cracks, leaving the conductor insulated only with the sleeving. The question then is whether that is an adequate replacement for the insulation.
 
  • Like
Reactions: DPG

Reply to Which conductor colours to use? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Wouldn't normally note this as an observation on a report but feel I need to. The way the building has been wired is all circuits on L1 have been...
Replies
6
Views
988
I’d appreciate your professional views on this question, as I’ve had 2 of the associated electrical bodies quizzed on this.!!!! ON changing/up...
Replies
13
Views
2K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
532
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
532
Quick Question. BS7671 specifies colour coding for 230V AC conductors, but I've looked through it and I'm sure I can't see anything which...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock