Presumably you are testing from live to earth here?

As it is a low impedance test it will be allowing enough current to flow through the tester to exceed the tripping threshold of the RCD.

Does it always cause an RCD to trip or has it happened with one specific RCD or installation?
 
Presumably you are testing from live to earth here?

As it is a low impedance test it will be allowing enough current to flow through the tester to exceed the tripping threshold of the RCD.

Does it always cause an RCD to trip or has it happened with one specific RCD or installation?
Hi Dave, thanks for answering, it happened twice so far with rcbo's in different houses when measuring voltage between active and neutral with the low impedance function.
Probably just very sensitive rcbo's, I was wondering if someone else experienced the same and see if there's a guess why.
Cheers!
 
Hi Dave, thanks for answering, it happened twice so far with rcbo's in different houses when measuring voltage between active and neutral with the low impedance function.
Probably just very sensitive rcbo's, I was wondering if someone else experienced the same and see if there's a guess why.
Cheers!

Why were you using the low impedance function to measure the voltage rather than a normal, high impedance, voltage measurement?

It may not be that the RCBO's are over-sensitive, it's more likely that there is already some leakage on those circuits and the additional current takes it over the tripping threshold.
 
Why were you using the low impedance function to measure the voltage rather than a normal, high impedance, voltage measurement?

It may not be that the RCBO's are over-sensitive, it's more likely that there is already some leakage on those circuits and the additional current takes it over the tripping threshold.
I was fault finding and at some stage used LoZ function to check ghost voltage, I looked for leakage with leakage clamp but there was none, I probably should have done a ramp test to check the sensitivity of the rcbo.
 
I'm assuming that you're using a multi meter such as Kline or fluke with a loZ function to do the measurement ?.

L to N should have been fine, L to E or N to E would probably cause the rcd to trip.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Australia
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
Australia
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Why does RCD trip when measuring voltage with LoZ function?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
nahuelparabere,
Last reply from
mainline,
Replies
10
Views
3,560

Advert

Back
Top