scott 123

Testing a ring final ..ze = 0.22
.r1 + r2 =0.65...
R2 +rn = 0.69
So calculated zs = 0.87
But when I test at sockets they are around 1.47
 
Testing a ring final ..ze = 0.22
.r1 + r2 =0.65...
R2 +rn = 0.69
So calculated zs = 0.87
But when I test at sockets they are around 1.47

By mixing use of upper & lower case "r" in your post, it is difficult to be sure what you mean.
 
  • Like
Reactions: 1 person
Testing a ring final ..ze = 0.22
.r1 + r2 =0.65...
R2 +rn = 0.69
So calculated zs = 0.87
But when I test at sockets they are around 1.47

Don't know what happened to my last post so here goes again, your r1+r2 result, is that the figure of eight result? ( R1+R2)
Losing it big time here the result of 1.47 ohms is that the average of all the sockets? or is it from one particular socket which could be a spur?
 
your R1+R2 should be (r1+r2)/4 i.e. approx 0.17. add that to 0.22 and you get Zs= 0.39.
 
  • Like
Reactions: 1 person
Don't know what happened to my last post so here goes again, your r1+r2 result, is that the figure of eight result? ( R1+R2)
Losing it big time here the result of 1.47 ohms is that the average of all the sockets? or is it from one particular socket which could be a spur?

Yes to the figure of eight and yes it was the average sockets were reading between 1.43 and 1.5
 
Is the ring a new installation or old. Contacts on older ring socket outlets can fur up badly if not used which could lead to high readings. Take a couple of readings from back of socket and compare.
 
  • Like
Reactions: 1 person
That is a little hard to understand Scott as, like the others have said, you've mixed up lower and upper case.

I find if anything when measured at sockets it can be 'less' then Ze + (R1+R2) due to Main bonding. Have you measured with a plug in tester? If so, it may be a good idea to use someones elses tester to see if you get the same results, or perhaps take the socket off and test actually on the conductors.
 
Last edited:
  • Like
Reactions: 1 person
As above, take readings from the terminals and not from the front of the sockets.
 
Yes to the figure of eight and yes it was the average sockets were reading between 1.43 and 1.5

In that case scott, your Zs was 1.5 I'm afraid :sick:. It's just gone up by another 0.03!
 
Testing Zs via a plug top lead can always give you false values even on new installs and why i rarely if ever use them. Test at the sockets terminals if you want accurate values that aren't relying on what is, just a scraping plug top connection..
 
  • Like
Reactions: 1 person
I'm a bit suspicious of ALL the readings being the same. Are you sure you nuled the leads and had the tester on the correct setting?
 
Are you testing on the no trip setting on your meter? In practice this rarely gives accurate results....usually higher than the actual value. I had this discussion with Megger after I found that my meter gave wildly variable results on successive tests on the same point.Their reply was that accuracy isnt that important on the no trip setting as the RCD means much higher values are acceptable anyway!!. Renders the no trip setting a little pointless IMO.
 
Agree with Wirepuller re the no trip!

Also when using the No Trip 15mA setting you can with certain RCD's get unusually high ZS readings due to the internals of the device.

Alarmbells should start ringing if the results are not what you expect and a futher bit of investigation work is needed to see if there is a problem!

Bypass the RCD and ZS the circuit from the DB using the 25A high current ZS test if in doubt!
 
  • Like
Reactions: 1 person
Agree with Wirepuller re the no trip!

Also when using the No Trip 15mA setting you can with certain RCD's get unusually high ZS readings due to the internals of the device.

Alarmbells should start ringing if the results are not what you expect and a futher bit of investigation work is needed to see if there is a problem!

Bypass the RCD and ZS the circuit from the DB using the 25A high current ZS test if in doubt!

This is going to start one of those debates....

It is exactly,what a competent tester could consider,as part of his investigation,but is frowned upon,by some assessors and instructors.

I reckon it is part of simplifying the instruction process,or one of a number of other reasons.

I have had this from trainers,and read this in many testing instructional books,but cannot see the difference between this "bypassing" and other bypass procedures,such as disconnecting bonding,for the purpose of a specific test.

One assessor i spoke to,concerning this anomaly,told me eventually "...well,bonding is one conductor,and one terminal..." and that bypassing any RCD,was "more involved..."

...Maybe it's just the same feeling of frustration,older dudes have,on finding some grads dissertation got a 1:1,with a spelling mistake on every other line,"coz,the content trumped it..." :icon12:
 
This is going to start one of those debates....

It is exactly,what a competent tester could consider,as part of his investigation,but is frowned upon,by some assessors and instructors.

I reckon it is part of simplifying the instruction process,or one of a number of other reasons.

I have had this from trainers,and read this in many testing instructional books,but cannot see the difference between this "bypassing" and other bypass procedures,such as disconnecting bonding,for the purpose of a specific test.

One assessor i spoke to,concerning this anomaly,told me eventually "...well,bonding is one conductor,and one terminal..." and that bypassing any RCD,was "more involved..."

...Maybe it's just the same feeling of frustration,older dudes have,on finding some grads dissertation got a 1:1,with a spelling mistake on every other line,"coz,the content trumped it..." :icon12:

I wonder if the OP had done an R1 + R2 on another circuit on the same RCD, and then done a Zs, to see if the higher reading was consistent?
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
zs unexpected results
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
scott 123,
Last reply from
Octopus,
Replies
15
Views
2,117

Advert