Discuss Zs values? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I want to find a table or something so I can see the Ka ratings as per different device type.Or at least someone to explain it in simpleton terms
on site guide and GN3 have tables with the standard kA ratings of all protective devices manufactures will give more details
 
0.06 seems low to me for Ze. if i am doing Zs on no trip, i usually do the Ze on no trip . no doubt someone will correct me on this, but i do it this way so as to make the readings same parameters as regards the test equipment.
 
Last edited:
why are osg tables 80% of bs7671?

When you do the Zs test the cable temperature will be around 20°C. The tables in the regs are the max Zs values when the cable temperature is 70°C.

As resistance increases as cables get hotter (0.4% per °C) you need to adjust the max Zs value for the lower temperature of the cable.

e.g The difference between 20°C and 70°C is 50 so the calculation would be 50 x 0.4% = 20% so the corrected max Zs values for 20°C would be 20% less than the ones for 70°C.

Hope that makes sense ;)
 
malcolm, could you clarify your last post please. say for a 32AMCB, the max. allowable value of Zs is 1.16, what you are saying is, if the circuit is RCD protected you enter 1667, not 1.16?
 

Reply to Zs values? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, I'm struggling with these questions for this circuit as the equations I have in order to work out impedance etc all seem to need the...
Replies
3
Views
295
Hi, I am currently reading through the standard IEC 61439-1 - Low-voltage swtichgear and controlgear assemblies - Part 1: General rules, and on...
Replies
0
Views
138
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
875
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
2K
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top