Just carried out an EICR on a standard semi which has had some work done in 2015-16. The works included connecting an outbuilding to the rear of the house to create a hall, WC and utility room. The Kitchen was also replaced, new cooker and shower circuits installed.

The 1 sockets circuit does have RCBO protection but is the only one!

Putting the other issues I found to one side, I wanted to know what others thought about this -

As I know the installation date was at a time the regs called for RCD protection everywhere, am I right to think this warrants a C2 for i.e. no rcd for cables >50mm on GF lighting circuit, just for a start..

If installed to 16th I would C3.

Naturally, client has no certs...
But - "he was very good and qualified.."
 
You inspect to the current standard on the day you inspect. Your inspection is a report on potential danger. Why is something classed as more dangerous for the same issue because of a different installation date ?
I would note on the cert that recent work carried out did not comply to the regulations and let the customer take that up with the installer.
 
As I know the installation date was at a time the regs called for RCD protection everywhere, am I right to think this warrants a C2 for i.e. no rcd for cables >50mm on GF lighting circuit, just for a start..

If installed to 16th I would C3
that would be a C2 for not having RCD protection up to the current 17th ,soon be the big blue book soon .
 
You should inspect to the 17th Edition AMD2 ...............

Clearly unsatisfactory.

Why are you doing the EICR?
 
You should inspect to the 17th Edition AMD2 ...............
If you're feeling really new-age you could even do it to the 3rd Amendment!
 
Something to consider, is the date of design.
An installation designed to the 16th edition can then be constructed some years after the 17th edition came into force.
For example the Olympic Athletes’ village in Stratford.
Designed to the 16th edition, construction completed in March 2015, some 7 years after the 17th was issued.
 
The sockets would be a C2 but for buried cables it would be a C3 for me.
so a hammer or a drill does not come in to it then David !
 
  • Agree
Reactions: 1 person
Another thing to consider: There is no requirement to provide RCD protection for cables concealed in walls.
It is just an option.
 
RCDs: protection of cables concealed in walls or partitions - http://electrical.----------/wiring-matters/54/cables-in-walls/index.cfm
 
Another thing to consider: There is no requirement to provide RCD protection for cables concealed in walls.
It is just an option.

Hum .... The issue I have with this, is simple, only the designer & installer will actually know how a cable is protected in a wall as any other form of protection may be completely hidden.

I asked another installer about why they had omitted rcd protection on 3 circuits recently. ...... They simply said that the circuits complied.... And didn't elaborate .... But anyone doing an EICR on a post 2015 property is going to code such a circuit as a c3 .....
 
So younthink cables buried in a wall are ‘potentially dangerous’ and the installation be deemed as ‘unsatisfactory’?

That is laughable.
read post #10,next!
 
Hum .... The issue I have with this, is simple, only the designer & installer will actually know how a cable is protected in a wall as any other form of protection may be completely hidden.

I asked another installer about why they had omitted rcd protection on 3 circuits recently. ...... They simply said that the circuits complied.... And didn't elaborate .... But anyone doing an EICR on a post 2015 property is going to code such a circuit as a c3 .....
That's why details of the design are supposed to be available for review when inspecting. (And of course I know how rare that is!)
 
Andy I always hear we can't condemn an installation that conforms to the standards at the time of installation but we are talking about an install that didn't confirm to the increased safety at the time. I get what you're saying "Why is something classed as more dangerous for the same issue because of a different installation date ?" But then why were the news regs bought into place?
 
Hum .... The issue I have with this, is simple, only the designer & installer will actually know how a cable is protected in a wall as any other form of protection may be completely hidden.

I asked another installer about why they had omitted rcd protection on 3 circuits recently. ...... They simply said that the circuits complied.... And didn't elaborate .... But anyone doing an EICR on a post 2015 property is going to code such a circuit as a c3 .....

It was clear from the switches I opened the cable was embedded in plaster >50mm
 
Something to consider, is the date of design.
An installation designed to the 16th edition can then be constructed some years after the 17th edition came into force.
For example the Olympic Athletes’ village in Stratford.
Designed to the 16th edition, construction completed in March 2015, some 7 years after the 17th was issued.

Another thing to consider: There is no requirement to provide RCD protection for cables concealed in walls.
It is just an option.

Thanks Spin, but your giving this guy too much credit...
 
I have this year converted my downstairs corridor lights to two way, cables concealed in oval conduit, no additional rcd protection and obsolete red, yellow and blue cable to boot:D
 
Andy I always hear we can't condemn an installation that conforms to the standards at the time of installation
Although that is an oft repeated phrase it is, nonetheless, incorrect.

Again I will use the examples of fused neutrals: these were permitted once, but that certainly wouldn't stop be from condemning them if I came across them now.
 
  • Agree
Reactions: Andy78
Although that is an oft repeated phrase it is, nonetheless, incorrect.

Again I will use the examples of fused neutrals: these were permitted once, but that certainly wouldn't stop be from condemning them if I came across them now.
As it’s BS7671 which states installations which complied with earlier editions, are not necessarily unsafe and do not require upgrading, citing instances that complied with pre-BS7671 Regulations is rather redundant.
BS7671 came into being in 2001 during the 16th edition.
 
I would give a c3 to a cable in a wall less than 50mm depth i certainly would not give a c2.

Sockets i might give a c2 but depends on other factors really, will eqipment be plugged in for out side use and stuff like that.
Problem here, is that there is no longer a requirement to provide RCD protection for sockets that might be used to supply equipment outdoors.
Would it be right to make an observation and apply a code for a non-compliance with a requirement from an earlier edition?
 
As it’s BS7671 which states installations which complied with earlier editions, are not necessarily unsafe and do not require upgrading
Nowhere does it state that they "do not require upgrading". What it actually states is that they do not necessarily require upgrading just because they don't comply with every respect with the current Standard. This doesn't give it carte blanche. It just means that due consideration must be given to the particular non-compliance and a safety judgement made.
 
Nowhere does it state that they "do not require upgrading". What it actually states is that they do not necessarily require upgrading just because they don't comply with every respect with the current Standard. This doesn't give it carte blanche. It just means that due consideration must be given to the particular non-compliance and a safety judgement made.
That is not what it means at all.
It means that just because the requirements have changed, it doesn’t now make it unsafe and it doesn’t have to be updated.
Remember, every new edition or amendment, allows an installation to be constructed to earlier editions after the new edition/amendment has come into force.
 
Problem here, is that there is no longer a requirement to provide RCD protection for sockets that might be used to supply equipment outdoors.
Would it be right to make an observation and apply a code for a non-compliance with a requirement from an earlier edition?

I thought reg 411.3.3 additional protection did require rcd protection for sockets not exceeding 20A and for mobile equipment not exceeding 32A for use outdoor, and that is in the new BYB
 
  • Agree
Reactions: JK-Electrical
Yes it requires RCD protection for sockets (that are not intended for specific items of equipment) and for mobile equipment used outdoors.
There is no longer a requirement to protect sockets that could reasonably be expected to supply portable equipment outdoors.
 
I know but in the best practuce guide 4 it says a c2 for the absence of a rcd for portable or mobile equipment that may be reasonable used out doors so if there was a lawnmower in the shed i would be able to reasonably assume that it will be plugged in so if that socket dont have rcd protection then the equipment would not have rcd protection.
 
Yes, that’s one of the problems with the BPG.
Inspect an installation to the current requirements then fail it for not complying with old requirements.
Follow that logic and we should fail due to lack of fuse in the Neutral.
 
Another thing to consider: There is no requirement to provide RCD protection for cables concealed in walls.
It is just an option.

Not 100% sure I agree with this.

So from the 18th does that mean we don't have to provide RCD's for socket circuit but we will have to for lighting circuits?
 
Yes it requires RCD protection for sockets (that are not intended for specific items of equipment) and for mobile equipment used outdoors.
There is no longer a requirement to protect sockets that could reasonably be expected to supply portable equipment outdoors.

Sorry, but I'm feeling a little lost :(
Hopefully the generality of the first sentence covers the loss of specificity of the second?
 
Last edited by a moderator:
  • Like
  • Winner
Reactions: Des 56 and Risteard
Andy I always hear we can't condemn an installation that conforms to the standards at the time of installation but we are talking about an install that didn't confirm to the increased safety at the time. I get what you're saying "Why is something classed as more dangerous for the same issue because of a different installation date ?" But then why were the news regs bought into place?

What are you using to verify the age of install ? If it's the customer's word then you can assume nothing. You have already said there is no paperwork.

What do you mean you can't condemn an install that complied at the time it was installed ? There are plenty of old practices and methods that are considered dangerous and should be coded. How the heck are you to verify the exact age of every install you inspect and whether it complied or not ? Do you carry round a copy of every single version of the wiring regs ?

My point is that if an issue is dangerous or not dangerous it does not matter when it was installed. It doesn't become more or less dangerous because of the presence or absence of a bit of paper.
 
What is the purpose of the EICR?

Is the customer trying to get a completion certificate off the council?
 
Finally,Andy got it:) The purpose of an EICR is not to carbon date,or time-team or do a character assassination on a previous installer...it is to assess,at that time,the condition of the electrical installation,and report.

As stated many times,two identical installation issues,could bring about different codes,or no code,in separate properties.

That is down to the opinion and judgement,of the inspector.
 
Spin, you said in a previous post:
EICR- Are Rcd's necessary ? - https://www.electriciansforums.co.uk/threads/eicr-are-rcds-necessary.108681/

""The socket may well be used for the mower.
However the mower may have an RCD plug, or may be used with a plug in RCD adapter.
The socket (unless it is intended for a specific item of equipment) fails to comply with current Regulations, as it has no RCD protection. To then make a further observation based on the fact that it fails to comply with something that is no longer a requirement of the Regulations, would mean that you are not conducting the inspection, in accordance with the requirements of BS7671.

If it is the case, that at the time of design/construction of the installation, the requirement to provide RCD protection for socket-outlets which could reasonably be expected to supply portable equipment outdoors was in force, then you have an installation which has never complied with the requirements of BS7671.
As such the requirement which allows for installations which complied at the time of their design/construction to not be deemed unsafe does not apply.
This would mean that a code C2 would be applicable for all general use sockets, cables concealed in walls, circuits of locations containing baths or showers, etc.""
 
What is the purpose of the EICR?

Is the customer trying to get a completion certificate off the council?

Customer is looking to purchase the home

Finally,Andy got it:) The purpose of an EICR is not to carbon date,or time-team or do a character assassination on a previous installer...it is to assess,at that time,the condition of the electrical installation,and report.

As stated many times,two identical installation issues,could bring about different codes,or no code,in separate properties.

That is down to the opinion and judgement,of the inspector.

I don't want to do that unnecessarily, this is why I'm asking for your opinions

There are also other issues like:

1.Sockets installed behind built in appliances with no isolation
2.Oven circuit - no isolator + hob ignitor wired direct to connection outlet
3.Main bond to water before stop cock - then plastic inline connector - no continuity present past the break, no supplementary bonding in bathrooms. (No code as it's now not an extraneous conductive part?)
4.Main bond to Gas not connected
5. IP top of CU, finger easy
 
You need to state facts and not worry about the whys and whens of any additions or alterations. Me personally I would reinstate the main protective bonds.
 
Sorry, but I'm feeling a little lost :(
Hopefully the generality of the first sentence covers the loss of specificity of the second?
It’s quite simple.
The requirement now, is for all sockets (except those for specific items of equipment) to be provided with RCD protection.
If you have a situation where there are sockets without RCD protection, you make an observation and code appropriately.
You don’t then add another observation because some of those sockets might be used for equipment outdoors, as there is no longer a requirement that specifies sockets used to supply equipment outdoors require RCD protection.
Mobile equipment used outdoors is required to be RCD protected.
That could be by means of an RCD socket, an RCD FCU, an RCD plug or an RCD plug in adapter.
 
  • Like
Reactions: Rpa07

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
EICR codes when RECENT works don't comply!?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
43

Advert

Thread statistics

Created
S P,
Last reply from
MFS Electrical,
Replies
43
Views
9,797

Advert