Just carried out an EICR on a standard semi which has had some work done in 2015-16. The works included connecting an outbuilding to the rear of the house to create a hall, WC and utility room. The Kitchen was also replaced, new cooker and shower circuits installed.

The 1 sockets circuit does have RCBO protection but is the only one!

Putting the other issues I found to one side, I wanted to know what others thought about this -

As I know the installation date was at a time the regs called for RCD protection everywhere, am I right to think this warrants a C2 for i.e. no rcd for cables >50mm on GF lighting circuit, just for a start..

If installed to 16th I would C3.

Naturally, client has no certs...
But - "he was very good and qualified.."
 
You inspect to the current standard on the day you inspect. Your inspection is a report on potential danger. Why is something classed as more dangerous for the same issue because of a different installation date ?
I would note on the cert that recent work carried out did not comply to the regulations and let the customer take that up with the installer.
 
You should inspect to the 17th Edition AMD2 ...............

Clearly unsatisfactory.

Why are you doing the EICR?
 
Something to consider, is the date of design.
An installation designed to the 16th edition can then be constructed some years after the 17th edition came into force.
For example the Olympic Athletes’ village in Stratford.
Designed to the 16th edition, construction completed in March 2015, some 7 years after the 17th was issued.
 
Another thing to consider: There is no requirement to provide RCD protection for cables concealed in walls.
It is just an option.
 
Another thing to consider: There is no requirement to provide RCD protection for cables concealed in walls.
It is just an option.

Hum .... The issue I have with this, is simple, only the designer & installer will actually know how a cable is protected in a wall as any other form of protection may be completely hidden.

I asked another installer about why they had omitted rcd protection on 3 circuits recently. ...... They simply said that the circuits complied.... And didn't elaborate .... But anyone doing an EICR on a post 2015 property is going to code such a circuit as a c3 .....
 
Hum .... The issue I have with this, is simple, only the designer & installer will actually know how a cable is protected in a wall as any other form of protection may be completely hidden.

I asked another installer about why they had omitted rcd protection on 3 circuits recently. ...... They simply said that the circuits complied.... And didn't elaborate .... But anyone doing an EICR on a post 2015 property is going to code such a circuit as a c3 .....
That's why details of the design are supposed to be available for review when inspecting. (And of course I know how rare that is!)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
EICR codes when RECENT works don't comply!?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
43

Advert

Thread statistics

Created
S P,
Last reply from
MFS Electrical,
Replies
43
Views
9,723

Advert

Back
Top