If your reply doesnt fall within the OP's question dont bother!
the op, is taking SWA has sub main to a new position and going to run it on the out side of the wall buried in render .me thinks it is bad idea .the op may has well run the SWA in the cavity if possible. or inside .
Then I cannot see why that RCD has been installed.
Thanks Essex,have been intending to look into this for a while this thread has just given me a kick up the arse,I believe it’s a 100a 100ma rcd main switch,not completely sure its time delayed I’ll have a look later
Reactions: Nigel
OP are you berrying the sub-distribution cable in the render as others are assuming that you are or are you cleating direct to render? What is your plan to run this cable?
No i am not burying in render it is my fault for the assumptions as i wasnt very clear, the wall is due to be rendered over and it will be cleated and ran along the wall, then drilled through into property.
Yes i havent ap
Ah my mistake ive just added the rating of the MCBs up
The old school rule of thumb is to exclude the highest rated circuit breaker, add up up the rest of the circuit breakers, times this figure by 0.4 and add this figure to the rating of the highest rated circuit breaker you excluded.
Reactions: Chris and telectrix
Yes i havent ap
The old school rule of thumb is to exclude the highest rated circuit breaker, add up up the rest of the circuit breakers, times this figure by 0.4 and add this figure to the rating of the highest circuit breaker you excluded.
  • Informative
Reactions: _ross and Chris
Thanks, it comes in at 76.8
What is the main REC fuse rating 100A? if so need 100A metal switch-fuse with 80A fuse.
Still learning!
Not a dig Chris but thought that you would have learnt regarding diversity prior to you doing 17th and 2391.
I often use the highest load such as a shower for example then add 40% of the remaining loads.
Similar to lees method maybe Just the formula transposed
Reactions: Chris
Yes main fuse rating is 100A, thank you.
And i know it wasnt a dig! I work for a housing association and havent done any maximum demand calculations since my college days.
Fair enough as said Pete said no profile anyway know where you're coming from now and yes if not doing all the things learnt at college you soon get rusty no offence meant Chris.
I would run a three core SWA the only thing if you are using 25mm is that the core that you are using for the earth it fits in the main earth terminal.
Reactions: Chris
Yes i only made this the other day i am yet to fill in all the details, will get round to it soon.
Yeah the supervisors do all the drawings and calculations so the rust appears to have set in haha! No offence taken.
That was my thought too im almost certain it will be too large for the MET i may have to figure something out for that.
I find multiplying by 0.25 a better calculation ......
Merseyside
Consumer unit to be moved away from service head
Chris,
Chris,