Had a quick call out to attend this evening. Currently closed but call was from a mum in need So I popped past with only my call out (light tools) in the car boot.

4 lights, one bathroom fan and a smoke alarm fed by a B6 MCB Protected also by an RCD.

Fault = no lights on the circuit working.
I quickly found the start and end of the circuit, so at the start I disconnected the loop so I could test the feed And work from light to light.
Using my fluke T5 the feed has the following:

Phase to earth = 240v
Phase to neutral = 35v
Neutral to earth 120v

the ceiling above is all a flat roof so no loft access.
I’m going back tomorrow for a proper look as I ran out of time.
Anyone had this type of fault before?
 
Lots of lost N's on here lately, must be catching.
 
You have a good apparent line to earth reading. Other readings are not so if you remove line and earth from your latter readings you are left with neutral.
 
  • Agree
  • Like
Reactions: JAWS and snowhead
Strange post indeed
 
Doesn’t sound all that strange at all.
 
  • Agree
Reactions: snowhead
Was looking at post details
 
I will bell it all out tomorrow, just seemed like quite strange readings.

Simply just ran out of time today and this was not a planned job.
 
Had a quick call out to attend this evening. Currently closed but call was from a mum in need So I popped past with only my call out (light tools) in the car boot.

4 lights, one bathroom fan and a smoke alarm fed by a B6 MCB Protected also by an RCD.

Fault = no lights on the circuit working.
I quickly found the start and end of the circuit, so at the start I disconnected the loop so I could test the feed And work from light to light.
Using my fluke T5 the feed has the following:

Phase to earth = 240v
Phase to neutral = 35v
Neutral to earth 120v

the ceiling above is all a flat roof so no loft access.
I’m going back tomorrow for a proper look as I ran out of time.
Anyone had this type of fault before?
Any IR testing done?
 
Think more will be posted today
 
Nope - I was in the car and only has my call out tool kit.
I'm off work, but responded for a quick look for a lady in distress.
 
70% of posts have been removed from this thread. If you wish to start a thread on the riveting aspects of snow tyres please start another thread.

Just chatting on while we wait for more details :-)
 
  • Like
Reactions: westward10
details to follow - I have not bee able to revisit as the lady has gone back to work, i'm going back on new years eve.
I have rigged her up some temp lights.
 
Must of been a nice few day over christmas then with no lights
 
As above, I rigged up some lights for her. also its only an extention thats affected so not the living areas.
 
Hoping for a update today on this
 
The OP I believe has established that it is the supply cable from the the CU to the first light point which is faulty.

Hopefully it will be a broken wire in the CU or a joint in between, not so good.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Strange Call Out This Evening
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
RED~SIX,
Last reply from
RED~SIX,
Replies
17
Views
3,791

Advert