No one likes not know the ending to a saga so here goes.

It turns out it was a lost neutral from the DNO side, which we originally suspected and called the DNO out for. They did earth loop tests on their cables but no dead test continuity, so when we returned in the morning we tested their side and we found the fault between the cut out and the meter.

We had been led down the wrong rabbit hole due to the DNO falsely confirming that the neutral was there, we originally tested our side but decided to test their side after we had called them out once already.

Some damage to a few PIR's, the roller shutter door controls, AC stats and a few other little bits but not as catastrophic as it could have been.

Thanks for the help guys.
 
With absolute respect to you fella, your Electrician should be able to understand how to test between phases and phases to earth and phases to neutral to determine if anything is amiss. The DNO supply is without doubt fine, the problem is your end, it is school boy stuff to test between cores, TNS and PME are types of earthing arrangement and nothing to do with a floating neutral which we believe may be the issue.
I didn't explain myself properly, the reason I mentioned the PME was because the DNO engineer did loop readings at the meter to prove the neutral was healthy, but because of the PME he was getting the loop reading from the earth when testing the neutral.
 
Glad to see a happy ending.

A strong sneeze would knacker a PIR, they seem to be sensitive to everything. Small single phase motors rarely survive a 400v blast either, but then neither would I 😂
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Northants
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Voltage spike causing strange readings?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
MdubElec,
Last reply from
KungFuTurkeyLeg,
Replies
22
Views
1,504

Advert