E
electricnova
Hi,
I have taken over a design engineering job for industry.
The design is using a 400V/110V transformer. Usually, the 110V is single phase. However, in this case it is giving 110V 3 phase 32A.
The 110v 3 phase is for use with 4P 110V socket to run a pump.
Being in the UK, I am used to seeing 110V single phase for this application.
Can someone explain why the 3phase option will have been chosen instead?
Any diagrams will be welcomed.
Thank you
Is the pump something specialised that's only available 3ph 110v?
Or is it in a Special location where the customer has specc'd 110v 3ph?
Hi, this information is not currently available - awaiting a customer reply. The pump is just a vacuum pump which we normally use single phase for.
I wondered if there were unknown reasons for use of 3 phase instead?
110V such as power tools on building sites are 110V split-phase...Not single phase
ie, there is only 55V to earth, but 110 between the two.
is it 110v between phases or 110v from phase to N?
a lot of equipment from Japan runs on (don't hold me to the numbers here) about 200v phase to phase, that gives around 115v phase to N.
not unusual in machine building circles but i don't see a reason for using it to supply a pump unless there is not an alternative available for 400v
Reactions: electricnova
Thanks. On all manufacturers data and our equipment schedules it is referred to as single phase.
Split phase and single phase (3 wire) I believe are the same.
55v to earth is the usual configuration with centre tapped to earth
However you can have the neutral to earth to have the full 110v to earth instead :) (this is the configuration in my original post)
Split phase is not the same as single phase.
split gives you 2 phases 180degrees apart.
single phase obviously has no phase difference angle.
3 phase has 3 x phase voltages 120degrees apart.
your original post is about 110v 3 phase
however you have just mentioned that you are talking about 110v from phase to earth is this 3 phase? If so then it would be about 200v phase to phase.
a drawing or spec sheet would be really useful at this point.
Reactions: nicebutdim
Sorry, I made an incorrect statement above.
I am looking to understand 3ph 110v.
However, this thread has made me question my understanding of 110v not 3ph (not sure what to call it at this point).
Why is it that manufacturers refer to 110v as single phase? I have attached examples
the voltage makes no difference to how many phases there are.
Thanks for your time.
I understand more now. I will ask my university lecturer to give me a full explanation. I just checked through my uni notes and we havent gone over any 110v applications.
To summarise my understanding.
The video explains a 400v 3 phase line will give the 230v single phase that we use in homes which i understand. And mentions the 110v single phase is from a 308v 3phase line (used in american homes).
So being in the UK with a 400V 3ph supply (230v single phase)... We add a transformer 400V 3ph/110V 1ph or 3ph, this means that the way we have achieved 110V is just through the step-down windings in the transformer with the secondary side either centre tapped to earth or neutral earthed.
Then we can either connect to one phase or three phase on the secondary side depending on the application?
Apologies for any complications along the way.
You can connect any single phase motor of the appropriate voltage to a 3 phase supply, either by connecting it across two of the phases or between one of the phases and neutral (if present).
There is actually no such thing as a single phase motor, since it would not start. Single phase motors use a capacitor to create a different phase and feed that to a second winding to provide a starting torque. After the motor is running the second winding as capacitor are often disconnected.
Single phase motors tend to be less reliable, more expensive and have inferior starting characteristics to three phase ones, so three phase is normally used when available.
ah yes, I recall this. I have only ever learned about 3 phase and so any mention of single phase I feel I don't have much understanding in a practical or theoretical sense. All I learned was how we achieve the standard 230v single ph really.
As for motors, again, only learned the 3 phase theory. Which coincides with your explanation of single phase motor as the rotation will need to be initiated. I imagine it to be similar to requiring a DC supply to a synchronous machine, in the sense of something being needed to start rotation.
Cheers
Note the terminology used in that table to describe the sockets: 2P+E or 3P+E, not 1P+N+E, and the requirement for protection to be DP or TP. This suggests that a single-phase supply derived from the 110V 3-phase is delta connected and both wires of the single-phase circuit are lines. This is the standard configuration for reduced low voltage 3-phase, 110V line-line and 63.5V line-neutral or earth, the highest permissible voltage classified as RLV.
As per @brianmoooore there is a definite advantage to using 3-phase for motors of any size, but increasing with the size of motor. If a particularly large pump is needed in this application, a single-phase option might be unavailable, costly or undesirable technically.
Ever since post #1, the reference to a 400V/110V transformer was really bugging me, as the 400V (I assume) is phase-to-phase, and 110V, while a familiar number, should in this context surely also be the phase-to-phase voltage, meaning, as you mention, the L to N is 63.5V. I wasn't aware that is a valid value, albeit the highest, for RLV.
Thank you for the contribution - I can now cease my puzzlement!
That is incorrect! Two phases 180degrees apart would give you zero volts phase to phase. It actually is single phase. A phase with the opposite polarity, i.e. 180 degrees apart, is not the same as a second phase. If you take a 110 volt secondary winding with a center tap and make the center tap ground or neutral, you now have a single, split phase. 55 volts from each leg to ground and 110 volts across both hot legs. If the two legs were not in phase with each other, then the voltage across both would be less than 110 volts.
  • Optimistic
  • Dislike
Reactions: Simon47 and DPG
1722529327837.png180 degrees apart. split phase.
Email
Time zone
Last seen
Purpose of 110V 3 phase?
Electrical Engineering Chat
electricnova,
Simon47,