AHU not working no idea of set up.. any easy fix on this FullSizeRender.jpegIMG_5563.jpeg
Have you checked the fuse :)
What is wrong? What have you tested? What external equipment is fitted and connected?
Power is there… not really sure on equipment connected… the remote control connections have no idea… is there anyway of overriding that marked RedIMG_7624.jpeg
You still haven't said what isn't working with the system.
Sorry …nothing working Fan not circulating seems like something a control may be holding the system off
How about the jumper settings, one is turned off in the first sequence, and looks like all are off in the second. Have any been accidentally moved?
No nothing been moved ...I can see … any idea of the correct settings on those??
No, I tried googling the make and model of the board and nothing came up so far.
The bit you circled doesn't see to match up with the colour coding on the diagram, I've used the jumpers as co-ordination for pasting in your board next to it.
Power is there… not really sure on equipment connected… the remote control connections have no idea… is there anyway of overriding that marked RedView attachment 109516
There's always a way to override things if necessary.
But you need to find out what controls are connected to it and check that they are working and set correctly first.
It does match the diagram, orange yellow and blue for terminals A, B and C which is a low voltage external control. Then two greys for X and Y which is a network connection for a centralised control system.
Reactions: cliffed
Fuse ok & lights flashing see pic belowView attachment 109518
How those three LED lights flash is a code to report a fault using the built in test functionality. Please could you describe and/or film what these three lights are doing.
This technical document may be helpful (pages 25/78 onwards) if your AHU series is covered within otherwise you could simply phone the UK technical help line:
http://www.toshiba-aircon.co.uk/ass...ols/New_Technical_Handbook_version_14_1_2.pdf
What are the full details of your AHU?
Further to my last. Page 77 of 78 gives support contact details and mentions a Toshiba app to download with the fault codes.
  • Informative
Reactions: freddo