Aug 22, 2023
63
24
83
Bridgwater, Somerset
I have a client who wants an EV charger installed, charger TBC, but about 7KW, installed about 20m away from this installation.
I've not done one before, but I understand I need to split the tails and main earth and add blocks so I can add an EV CU.
CU is in a cupboard and the tails and earth must be coming up from below it, would you look to add the blocks/EV CU in the meter cabinet or near the current CU? (put a bit of ply on the wall to mount on?)
I'd appreciate any advice or guidance, and if anyone can explain what the PEN issue is and what I need to do/look out for when selecting materials.
Reactions: Admin
start in the beginning 20m to where. and what about the charger has it a built in rcd.and how you going to install the cable ect ect.
Reactions: tony9i9i9i
Hi Buzz, thanks for responding, the client shortlisted 4, although he did say he wanted an untethered one. So on the basis that Zappie V2.1 7kW (ZAPPI-2H07UB-G) ticks all the boxes, I'd say that one.
It has pen fault protection and "Socket Protection" includes - "Overload, DC Sensitive and Fault Current Protected" so yes rcd.
Supply is in the house, and the charger is to go on the outside of the garage wall, so the run will be part clipped direct, and part buried underground.
Read the attached file first and work out how you are going to install it simples .
Not necessarily. See below.
You need to check whether it is looped supply. If so, stop, and apply to connect.
You need to know existing max demand. If the house routinely pulls more than 60 amps (and it has an 80 or 100 amp service fuse) then stop, and apply to connect..
Otherwise you can crack on and install a charger that will throttle the charger if the grid limit exceeds 60 amps, and then tell the DNO you've done it.
Choosing a charge point that has built in double pole RCD protection including 6ma DC leakage protection makes this simple as at the CU it can just be an MCB in an existing consumer unit and armoured cable (so impact protection rules are met).
You'll need a CT clamp around the meter tails, so will need data cable to the charger too, or use one of the products such as EV ultra that has data within it.
Assuming it's TNCS earthing, you basically have a choice between isolating the earth at the charger and sticking an earth rod in, or connecting the CPC as usual and using a charger with PEN fault protection.
A PEN fault is when the combined Neutral and Earth supply conductor get's broken. This can create a very dangerous condition where all metalwork becomes live, and a person completes the circuit to earth. It's generally not so serious inside a house (vast simplification) but as cars live outside, it would obviously be pretty lethal to have a car body at a potential of 230v. Hence the PEN fault protection issue.
I've not done many of them myself but believe the above summarises most of the pertinent points.
There's quite a bit more to installing an EV charge point than meets the eye. That's why there's a whole section in the regs and also a code of practice that should be followed. I would strongly recommend you get hold of a copy and study it before attempting to install one.
I admit I don't have the code of good practise. £73 is a bit above my impulse purchase threshold.
Would you say it's a practical and sensible document?
The reason I ask is that I reckon the 4 pages of regs and 2 pages of appendices are among the harder pages in the book to turn into practical reality as there seem to be several wild-goose-chase pathways that are unlikely to ever work in practise.
e.g. In my opinion, TN Indent ii is a waste of space. Single phase with 40 amp max demand you end up needing an additional rod with Ra under 2.5 ohms (and it only gets lower as the demand goes up), and the three phase calcs happily come out with a negative Ra to beat. (The original 18th edition 3 phase logic worked, but they messed up the logic in amendment 2 which stops you using the formula with smaller neutral currents.)
I doubt anyone can be making use of this clause. It's much simpler to TT the charge point or use PEN protection methods instead.
But my main question, is the code of practise helpful and worth having?
Certainly worth it. It goes into great detail as to all the different charging modes, connection types etc.
Then there's a summary of the legislation relating to charging equipment.
There are risk assessment templates to follow with regard to choice of earthing arrangements.
Practical diagrams as to location of charging equipment relative to parking spaces.
Recommendations for protection against vehicle impact.
Accessibility and part M.
Clear diagrams explaining things like touch current.
Full explanations of the various methods of PEN fault protection.
Appendix on installation of earth electrodes.
Detailed instructions on inspection and testing.
On street installations. Commercial installations.
Vehicle as storage.
How and when to notify DNO.
Checklists for the different types of installations (dwellings etc.).
Explanation of the consequences of not providing adequate separation between PME and TT earthing systems below ground.
And lots more ...
Regarding your query
The code of practice states that achieving a suitably low value is generally not practicable.
PS.
The code of practice was recently updated to version 5, consisting of 208 pages with many diagrams and charts.
Are saying car charging practice up dated 5. Cost about £85.00 quid on IET
Webb page.
One last question, when working out the load on the installation and adding the EV Charger, can you apply diversity to the charger?
No you don't need to it's like having a 7kw shower. Is the ev charger add load to a consumer unit or separately.if you have a 60-80amp fuse it need up guarding to 100amp.
I've done a bit more research. It's a 100 Amp Supply, split consumer unit with AC RCD on both sides. So will install a separate CU with double pole Type A RCD and surge protector to feed Wallbox Pulsar Max which has the RDC-DD and PEN fault detection built in.
Reactions: buzzlightyear
[GALLERY=media, 29034][/GALLERY]
Watch.
(Edit: I've added the video to our website, and then used the embed feature on the media item to add it to the thread - Trying to make it even easier too... baby steps. Dan)
You could fit DP type A RCDS in the existing board... or as a lot of hager boards dont have a neutral bar could fit on at the top and run a MCB on its own next to main switch and run it through a Type A RCD then on to the charger. although if the charger has built in rcd protection via the RDC does the manufacturer specify a DP type A still? I would personally still fit one as its dubious if some of these chargers actually comply to the regs.
There are a 100 ways to skin a cat and no two EV installs are the same. Having done 100s of them you learn something different on each one. It is only with experience that you can look at a consumer unit and see a solution.
Are you a registered Zappi installer or registered with any EV manufacturer...if not cannot carry out the works as you wont be able to commision the work
Yeah gone with Wallbox and did their online training yesterday, I'm certified and certificated!:)
I did the Wallbox training a while ago. Mind numbing comes to mind!
In case you can't find it, as I couldn't, the bit covering the installation of CT clamps is part of a separate online training course called "Metering" or similar.
You can say that again, it's like sitting in a dentist chair waiting for anacetic to go off before they pull you teeth out after.
Top Man Does that cover any other manufacturers or just wallbox
In the old days of the OLEV grant we used to have to send proof of manufacturers' approval for each different make & model of chargepoint we could fit under the grant. Of course each manufacturer insisted on doing their training first...
I hope you don't mind me jumping on the end of this thread with a query as I see it's occupied by the correctly qualified folks. I've just had a quote to run a supply to a charge point (7kw) about 20m to the end of the garden.
Unfortunately the easiest route from the CU is through the home via the the loft and out the back. I'd obviously expect armoured cable to be used in the garden but is it a requirement in the loft as I've been told? TIA
Depending on length of run, it’s probably cheaper running one continuous armoured cable than having a joint from armoured to non armoured half way… and that would be introducing a possible fault point at a joint box.
However, if you choose a cable with the additional comms cat5 built into it, the cost per metre increases.
Can you give us the figure and we could judge whether it seems realistic or not.
The run is about 12m internal and 15m external. I'm not particularly querying the price atm as it's my first quote just wondering if it was strictly necessary due to regs but then it isn't drawing anymore than a low powered electric shower. No CAT5.
Quote was just under £1800, suburbia Uxbridge nr Heathrow.
I know London-ish prices are much higher than the rest of the country... so i dont think its too bad...
Regulation wise, then no... you wouldnt need armoured within the house as it doesnt need mechanical protection as it does outside. You also cant run standard household flat grey twin and earth outside as the UV from the sun can damage the insulation.
Try running your "low powered electric shower" for several hours a day, non stop.... thats more like an electric charge point.
Reactions: gmartine
The Mrs likes very long showers but I take your point . :) Tnks
Just a thought as you mentioned integrated CAT5, do chargers need to be able to connect to the interweb?
There is a requirement for them to be “smart” but that can be done over Wi-Fi.
A few may need internet access for set up, but then can be disconnected from internet and turned dumb
Reactions: gmartine
Sounds very cheap for that to me. Certainly I would charge more for that.
I would have expected data cable at least for load curtailment purposes however.
Me again, getting varying answers as to how deep the armoured cable needs to go (along side a concrete path and lawn). Octopus have said 600mm, online search says 400mm and an eng came round and said what I've dug so far is ok - 100mm. Anybody have a definitive answer? TIA
Deep enough as to not be damaged through normal traffic.
So, not very deep if no traffic….. a bit further down if lawn that gets walked over…. Deeper still if light vehicular traffic….
Down deeper if under a ploughed field.
Although 100mm doesn’t sound deep enough in your case if area likely to be dug up for flowerbeds or weeding.
Remember it would need to be bedded in sand… even armoured cable can be pierced by sharp stones/ gravel whatever.
Reactions: gmartine
If they want it at a minimum of 600mm depth then that is what you need to do. Anyone else's opinions aren't relevant.
EV charger installation 7KW, installed about 20m
Electric Vehicles Advice Forum
tony9i9i9i,
gmartine,