Discuss Dangers of ring final circuit in the Australia area at ElectriciansForums.net

Baker1988

-
Arms
Reaction score
360
Hi i have been set some home work from college to find out why ring final circuits are dangerous. I know the obvious that if one leg on the ring breaks it will not be a full ring and the 32 amp mcb will be too big for the cable as it will only be able to carry about 20 amps with out it been a ring which would over load the cable. But i can not find any thing other then what i already new can any one help me with this
 
Hi amp david it was my tutor at college that is what he set for home work he said they are dangerious and asked us to find out why i did not think they was dangerious as if they was why would we use them in this country where health and safety is a big part of every thing we do
 
But how does been uneducated make a ring dangerous? And also he may be doing it as a trick or something to try and get us to learn more about ring final circuits
 
the question should of been to find the advantages and disadvantages of a ring final circuit. The question your tutor has set is very leading, and hes tryinmg to force his opinion on you.

IMO education should be about giving you the hard facts, and knowledege for you to make your own decsions.
 
And also he may be doing it as a trick or something to try and get us to learn more about ring final circuits

I can only hope this is the case.

As you've said, the biggest risk would be if the 2.5/1.5 RFC were to 'break' and thereby become 2 radial circuits, each protected by a 32A OCPD which as we know would be above the CCC of the cable.
 
Go back to your tutor and tell him they are not exlcusive as far as danger is concerned

A ring final has the potential for danger, as do all incorrectly operating circuits and just about everything else in the electrical industry

Find some reasons why, when the design of a ring is abused, where problems can arise
Present them as potential problems for a circuit described as a ring, but not installed or operating as such
 
Yes i already know the advantages and disadvantages as i have been looking this up for the past few days and have learnt loads of stuff about rfc but could not find anything about dangers So is my tutor wrong? are they not dangerious? Is this his personal appinion
 
Yes it is. A cable is dangerous if its damaged, but we still dont label them as such. Any circuit installed incorrectly can become dangerous.The one thing all circuits ahve in common is that one of three things are required for them to become dangerous.

Intervention
damage,
or natural degradation
 
Hi amp david it was my tutor at college that is what he set for home work he said they are dangerious and asked us to find out why i did not think they was dangerious as if they was why would we use them in this country where health and safety is a big part of every thing we do

The only thing ''Dangerous'' here is Yet another numpty so-called lecturer that's perpetuating his ''OWN'' personal misguided views and prejudices onto his students. All this does, is burden these students with the myths and scaremongery we see all the time, in newly trained or trainee's in the posts they write .... I suppose this same lecturer tells you that you can't use the armour of SWA cable as your CPC too, or you Can't extend a PME earthing system from the house to a garage or shed....

And we wonder why these students are leaving collage/training centre's, with little or no idea of circuit design. Makes you wonder if it's these lecturers that are in dire need annual assessment, on their competency to teach, ...Just like the majority of the Part Pee electricians that were taught by these numbties....
 
so are you saying that the original point made by baker1988 is not correct?
ie. a break in the ring will not be detected by the user so the ring could be operating beyond the cable capability. In this respect it could be considered more dangerous than a radial could it not?

Just trying to understand the situation myself....
 
so are you saying that the original point made by baker1988 is not correct?
ie. a break in the ring will not be detected by the user so the ring could be operating beyond the cable capability. In this respect it could be considered more dangerous than a radial could it not?

Just trying to understand the situation myself....

As I said in post #7, that is the biggest risk of an RFC, as the householder would not be aware of it so the cable may if heavily loaded, be operating outside of it's capacity.
 
what would cause a break in the ring, other than manual intervention? Maybe rodent damage, or drilling though a cable, but that would cause short circuit, which would operate the potective device.
 
I totally agree with you E54,
Ive lost count the amount of times i have been on the phone to my son's college about the poor teaching and wrong information they are pumping out, the best one was that asbestos does not exist in any type of switchgear and i should know as ive been on the tools for 15 yrs, believe it or not this was from a H&S lesson.
 
what would cause a break in the ring, other than manual intervention? Maybe rodent damage, or drilling though a cable, but that would cause short circuit, which would operate the potective device.

Number 3 on your list John.

Although a million to one shot, conductors becoming loose at their terminals over time 'could' cause a situation as described which may go unnoticed for a good length of time.

Highly improbable for both L&N to work loose but........
 
I think you guys are taking this a little too serious.

I've asked similar a question to my students before, not necessarily that rings are dangerous, but more about there opinion to the potential dangers a ring final can create when under the control of "ordinary persons".

and the answer is YES. Ring final circuits are more dangerous.
 
Number 3 on your list John.

Although a million to one shot, conductors becoming loose at their terminals over time 'could' cause a situation as described which may go unnoticed for a good length of time.

Highly improbable for both L&N to work loose but........

fair point lenny. is this more dangerous than any terminal working loose though, lets face it either a loose live, or neutral will probably cause a fire or burning on any circuit, long before it works completely loose.
 
As I said in post #7, that is the biggest risk of an RFC, as the householder would not be aware of it so the cable may if heavily loaded, be operating outside of it's capacity.

So you did. Which is why am puzzled that the lecturer is getting abused for asking a question that has a valid answer.
 
if i read the op correctly, the question was "why is a ring final circuit dangerous?", not "how may a RFC become dangerous"?. apart from a leg going O/C, there is the potential for the 2 legs to be fed from different OCDs. that would be dangerous. but, as has been said, it's a potential danger, not an inherent danger.
 
An unbiased view of advantages and disadvantages of Ring versus Radial.

Note:- In the following list of advantages and disadvantages of Ring and Radial final circuits. Some points are followed by a question mark because supporters of each type like to argue their best case, but it like most things in electrical engineering it’s not really "black and white" it depends on what is compared with what.

The Ring Final Circuit Camp argue the 32A, 2.5 T+E, Ring Final Circuit versus the 32A, 4 T+E, Radial Final Circuit.
Whereas the Radial Final Circuit Camp argue the 20A, 2.5 T+E Radial Final Circuit versus the 32A, 2.5 T+E, Ring Final Circuit.

Advantages of the Ring Final Circuit:
1) It reduces the amount of copper used in an installation?
2) It reduces the number of circuit protective devices
3) It helps to reduce voltage drop
4) It has proved its value over the last 60 years
5) It promotes sustainability in design
6) It is good for the Environment?

The disadvantages of Ring circuits are numerous:
1) Compliance with Regulation 433.1.103
2) Not understood – lack of training of electricians from other countries
3) Susceptible to fault conditions
4) Testing and fault finding is very time consuming and costly
5) Fault conditions are not apparent when in use
6) Use more cable and take longer to install compared to 20A Radials – waste of resources?
7) Generally not cost effective compared to 20A Radials

Advantages of Radial circuits:
1) Greater flexibility
2) Less cable would be needed
3) Less time to install
4) Lower installation cost?
5) Less drain on the world’s resources of copper?
6) The problems created by Regulation 433.1.103 – distributing load evenly in a ring circuit (that nobody takes any notice of) would disappear thus reducing the exposure of the contractor to a breach of regulation claim.
7) Considerably less time required for inspection and testing.
8) Less likelihood of installation faults
9) Any breaks or loose connections will be readily identified when testing.

Disadvantage of Radial circuits
1) More circuits required
2) Larger distribution boards
3) More circuit breakers required
 
I seem to remember when I was doing the 16th Edition an college, the lecturer said he preferred Radial circuits over Ring Finals because he felt that there was a greater potential for danger with RFCs.
 
If you look and study this list of advantages and disadvantages, there are some blatant contradictions.... In fact i'd go as far as saying there is not much evidence here to say this list is ''unbiased'' at all!! Into the bin with it!! lol!!
 
not at all. Quite the opposite. I am just puzzled that the lecturer got a lynching for getting his students to think about why they might not be perfect. ;)

Because he is WRONG to suggest RFCs are dangerous, they are not, and never have been. They can only become dangerous by interference, the same way any other circuit can...
 
the question should of been to find the advantages and disadvantages of a ring final circuit. The question your tutor has set is very leading, and hes tryinmg to force his opinion on you.

IMO education should be about giving you the hard facts, and knowledege for you to make your own decsions.
yes....he`s clearly of the "anti ring final" camp.....rather than take his head out of the sand and realise that both ring and radial finals have their advantages and disadvantages ant the fact that you should assess the situation first....and then decide on the best course of action...such as ring or radial...diversity applied....MCB and type and CSA of cable to use etc.....what this lecturer is doing aint on....he`s trying to sow the seeds of doubt here in regards to what is a safe and recognised wireing system......
 
An unbiased view of advantages and disadvantages of Ring versus Radial.

Note:- In the following list of advantages and disadvantages of Ring and Radial final circuits. Some points are followed by a question mark because supporters of each type like to argue their best case, but it like most things in electrical engineering it’s not really "black and white" it depends on what is compared with what.

The Ring Final Circuit Camp argue the 32A, 2.5 T+E, Ring Final Circuit versus the 32A, 4 T+E, Radial Final Circuit.
Whereas the Radial Final Circuit Camp argue the 20A, 2.5 T+E Radial Final Circuit versus the 32A, 2.5 T+E, Ring Final Circuit.

Advantages of the Ring Final Circuit:
1) It reduces the amount of copper used in an installation?
2) It reduces the number of circuit protective devices
3) It helps to reduce voltage drop
4) It has proved its value over the last 60 years
5) It promotes sustainability in design
6) It is good for the Environment?

The disadvantages of Ring circuits are numerous:
1) Compliance with Regulation 433.1.103
2) Not understood – lack of training of electricians from other countries
3) Susceptible to fault conditions
4) Testing and fault finding is very time consuming and costly
5) Fault conditions are not apparent when in use
6) Use more cable and take longer to install compared to 20A Radials – waste of resources?
7) Generally not cost effective compared to 20A Radials

Advantages of Radial circuits:
1) Greater flexibility
2) Less cable would be needed
3) Less time to install
4) Lower installation cost?
5) Less drain on the world’s resources of copper?
6) The problems created by Regulation 433.1.103 – distributing load evenly in a ring circuit (that nobody takes any notice of) would disappear thus reducing the exposure of the contractor to a breach of regulation claim.
7) Considerably less time required for inspection and testing.
8) Less likelihood of installation faults
9) Any breaks or loose connections will be readily identified when testing.

Disadvantage of Radial circuits
1) More circuits required
2) Larger distribution boards
3) More circuit breakers required
what do you mean at 9 on the radial list here Markie?.....so you dont do an r1...r2...rn...on a ring final then?...
 
Just think,in not so many years, the warning to the customer off some will be, "they are against the law and needing ripping out"

It may give the Wylex fuse boards a bit of a rest
icon7.png







Only joking by the way
icon6.png
 
the question should of been to find the advantages and disadvantages of a ring final circuit. The question your tutor has set is very leading, and hes tryinmg to force his opinion on you.

IMO education should be about giving you the hard facts, and knowledege for you to make your own decsions.

I was trying to think up a reply then i read yours. Spot on mate, couldn't agree more.

Cheers............Howard
 
I think you guys are taking this a little too serious.

I've asked similar a question to my students before, not necessarily that rings are dangerous, but more about there opinion to the potential dangers a ring final can create when under the control of "ordinary persons".

and the answer is YES. Ring final circuits are more dangerous.


Yes, we know your opinions on RFCs Your one of these Lecturer's impart and burden your own prejudices on your students, instead of giving the hard facts and knowledge for them to make up their own minds...

There is nothing Dangerous about an RFC, that has not been tampered with!! As far as your students go, keep your own opinions and prejudices to yourself!!! The last thing this industry needs is your personal prejudices being perpetuated along with all the other myths and scaremongery that's out there...
 
Ring finals are great. It’s when the know nothings come to fault find on them they become a problem! And BTW if I were to do a house rewire I’d still do the lighting in a ring. OK I’m a bloody dinosaur but I’ve never gone back to a fault of my making.
Radials are for the know nothings that can’t do simple calculations.
 
The bottom line here imho is, as long as you have done the calcs and proven the installation is ok, and as long as no one has buggered about with them andit's been tested properly it does not matter whether the circuit is a radial or a ring it'll be alright
 

Reply to Dangers of ring final circuit in the Australia area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi there I am struggling with the following calculation. 4mm Ring Final Circuit, In = 32A Cg - group of 6 with a correction factor of 0.57 Ci -...
Replies
10
Views
2K
Hope you're all well . I've had ring door bell 2nd generation hardwired for 1.5 yrs... it was connected to transformer which is connected to the...
Replies
22
Views
1K
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
359
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views