Hello,
I need some advice, I have wired and fitted 2x down lights with 7w Kosnic LED lamps. These are switched from 3 positions. They are on a circuit suppling 13 other down lights all with LED lamps. (All the wiring is new as it's a renovated house, which I've wired).
Now testing the conductors of the cables with the megger all tests are fine and clear. When the circuit is energised the lights work as they should (I have done this sort of thing before!)
When the light switch is in the off position the lights go off, but then 1 down light starts to flash intermittently.
I have tested at the light fittings and I'm getting 74v with the switch in the off position???!!!???
Can anyone help me with this little set-up? I have been tugging my hair out today trying to figure it out!
It's not a loose neutral, as all neutrals are connected with Wago's (Helacons). And I have taken the light fittings out of the circuit.
I have also had all the switches off and connected the wires together with Wago's but still getting the same voltage.
I'm starting to think I'm going mad, but I know that happened along time ago!
Could it be induced voltage in the 3core between the switches? I have turned off all circuits apart from this one so I know that it's not coming from anywhere else.
If it is induced voltage can I loose it somewhere using something? I have been thinking of ferrite magnets? But I don't know that much about them.
Could it also be the lamps? Has anyone had anything sililar happen to them?
Sorry to go on but it helps to get it down on the screen.
Cheer
Billy
I'm not certain but I seem to recall someone on here saying the lamps have capacitors in them , so could be discharge?
I have led plinth lights and the misses sees them flash occasionally
induced voltage. this can be improved by fitting a snubber ( or more than 1). across the sw L and N on each group of LEDs.
I also thought it could be a discharge, but not all of the down lights do this. Could it be because there is only two on this sw line?
Could it be the lamps? they're not the cheepest, but I have had problems with the Kosnic 5w dimmable range.
dont think its because you have two, have you checked the other fitting for any voltage?
Hi, What is a snubber and where do I get them from?
it's a resistor and/or a capacitor combination. there are various ones. it has been suggested that a 330K resistor across L and N terminals in the one of the fittings might do the trick. a bit of trial and error involved. have you tried measuring the voltage with an analogue meter. ?
well, nick's just suggested 1 Meg. that's the trial and error part. try 1 Meg., and if it's no improvement, try a lower value. ( not too low, of course ). the combined R/C snubbers may well give a better result.
ive noticed on here recently problems with leds staying on when switches are off not had any problems my self and fitted quite alot whats the general feeling of why there staying on just in case it happens to me look a fool if you cant tell customer why its happening
Just trying to re-ignite this one as I'm back there tomorrow to have a go at it.
I'm going to start by taking all the LED lamps out of the circuit, and test again for the voltage. If it is still present (which I'm sure it will be) I'll then start taking the circuit apart.
The thing that is bugging me is that with ALL the light switches of the circuit off, I still get 74v at this particular down light fitting. And I also get approx 58v at the bathroom light fittings.
As said before all the neutrals are in Wago's, the wiring is new, all the conductors are meggering at >499 (I tested at 1000v to make sure). I've meggered the switches, taken the switches off and connected the wires into Wago's.
ANY ideas would be good just for me to try them. The more I think about it the more confuddled I get.
Many thanks for taking the time to read this.
if it's induced voltage you won't be able to fix it as long as cables run together.
Do you really think it could be an induced voltage of 74v?? and coming from the black strapper to the grey strapper but by-passing the earth wire?
Quite possibly. We're guessing you effectively have the equivalent to this as the overall circuit: http://cappels.org/dproj/simplest_LED_flasher/Simplest_LED_Flasher_Circuit.html with the 3 core for the two way lighting behaving as the capacitor.
The length of one of the strappers will dictate how high a value capacitor you in effect have (the longer the run the higher the capacity) and hence the PD present. You'll find the timing between flashes is a regular period (if only a long time between flashes).
The addition of a snubber resistance will increase the overall resistance to the point where there is insufficient current flow for the led lamps. It can eliminate it completely (but too high a resistance would mean no current flow at 230V either!).
So in this particular case probably not induced from an adjacent circuit, rather from that same circuit; so the only other way to eliminate it would be to run the strappers and common separately (separated by a greater distance, so then no capacitance build up).
did have a problem with commercial hair dryers giving the user a shock when they un plugged them , the suppression capacator was across the incomming side of the switch so was holding charge after it was switched off an zapped any one when unplugged and they touched the pins easily rectified 20 hair dryers later relocated the capacator to the other side of the switch , and wrote to the manufacturers too
Thank you all for your replies. All were very helpfull. I understand now that it is probably induced/capacitance voltage and that the only way to get around the problem is to use a resistor/snubber. Could anyone point me in the right direction of the size that I would need or a calculation to work it out.
Am I right in guessing that it is Ohms law? I have the voltage (74), but I have no current and therefore no way of working this out at the moment.
many thanks again
Depends on the lamp spec (ie min current), I'd go for a 2K7 Ohm resistor, if you've got to buy some then buy a set of standard values. If you think about it you do have a current, the spec of the lamp is 7W (at 230V).
Do you have a dimmer on the lights? I fitted led's back when they were still very new and the dimmer actually lets a little voltage past and the lights never went all the way off. Could only be seen at night though but it was twinkling.
joking appart what would be an idea is to do a complete test on the circuit r1r2 ,r2rn etc etc this voltage could well be caused by a fault or underlying fault so could be well worth checking
Hi Joe, no dimmers on this circuit or any circuits in the house for that matter. No electrical control gear anywhere either.
It is definitely a capacitance building up (if thats the right way to think about it) on the strappers. I have done all tests possible (R1+R2, R2/R1/RN, Meggered at 1000v between all conductors on the 2way intermediate strappers. Removed all LED lights from the circuit and Meggered the complete circuit again. Disconnected the earth bond to the gas/water to see if I was getting anything from those. Tested for voltage on the water pipework in the house (altough all plastic apart form airing cupboard).
I have litterally been over this with a fine tooth comb, and this is the only thing that it can be. I would like to resolve the issue of the capacitance but it is a no-no as the house is now finished and chasing walls is out of the question.
I even removed the strappers and common from the switches at both ends of the 2way, and connected one strapper (black) to the live, and then tested for voltage at the 2nd 2way switch. I was getting 105v on the common (brown) and 60v on the 2nd strapper (grey).
I then isolated the circuit, put it all back together, and put a 2K2 resistor between the switch live and neutral (at the switch) this stopped the 74v which I had at the fittings, the only problem was it glowed red hot when the switch was on and suppling the fittings. Obviously it can't withstand the 240v running constantly through it.
Could anyone give me a clue on working out the size of resistor that would be needed?
It needs to be able to allow the 74v through it to neutral, but not allow the 240v to do the same.
So would a high resistor i.e 1M or above do this?
God my brain is fried......Please help.....
What rating of resistors did you buy? That 2K2 resistor is going to be dissipating about 25W when the lighting is full on. It should be rated at 250V and around 35W to be safe. Perhaps I should have stated that.
I was in RS and in a hurry, so I brought some 1k and 2k2 both of which are rated at 3w! No wonder it was getting a bit warm. I'm going to look at the RS website now to see if I can find the ones you recommend.
many thanks for your advice, much appriciated
I'm probably barking up the wrong tree entirely, but have come across induced voltage problems before, which seem to have been caused by a disconnected cpc, 90-100V in one case. Have you checked the cpc?
Thanks for the advice Jeremy, but these have all been checked and cheaked again. Getting the voltage on the brown/grey when not connected to anything is definitely pointing to the conductance.
Limited choice on the packaging front. I'd probably go for this given your 2K2 Ohm choice: Buy High Power RESISTOR 50W 2K2 Vishay RCH50S22000JS06 online from RS for next day delivery.
Easy to solder some leads on for use and wrap in heatshrink for use. Should be easy enough to incorporate in the box(es).
Hi, I managed to get hold of these and they seemed better than the first lot I got hold of, I wired one up to a plugtop to see how hot they got. It lasted for about ten minutes, didn't get too hot, but then burnt it's self out.
Speaking to someone at the wholesaler and they have suggested that I could put an SES lampholder with a oven lamp in the ceiling void which will take the excess voltage out of the switch live.
Good Idea??
I'm not too sure. It would probably work but I dont fancy leaving something like that in the celing...
Is there any other suggestions that anyone can come up with?
Burnt out? What did you use as a heatsink?
Errrmmm?? Nothing....
I just left it on the floor, to do it's merry business. It expanded slightly on the back, then it cracked and stopped working.
I really have no idea with this. I wouldn't have thought it needed a heatsink as surely it would have said it needed it on the paperwork?
Data from the spec:
Power at 25°C50W with heatsink, 5.5W without heatsink
Resistance Tolerance±5%
Temperature Coefficient≤1Ω ±250ppm/°C, >1Ω ±150ppm/°C
Operating Temperature-55°C → +125°C
Thermal Resistance1.0°C/W
Limiting Element Voltage1285Vac
Overload Voltage2500Vac (Max.)
Dielectric Withstand Voltage3.5KVac
Insulating Resistance10000MΩ
Length50 mm
Width29.4 mm
Height15 mm
Reply to Voltage at light fitting that is turned off in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi all. Removed an ancient light fitting, replaced with a newer one, the light comes on but can't be turned off with the switch. It was working...
Good Morning need some advice please. Yesterday went to change a light fitting in hallway. There are two ceiling lights in the hall controlled by...
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Hi Just replaced a bathroom extractor fan. I didn't alter any wiring. Both old & new have live & switched live. Trouble is, once activated, the...