Will the temperature around the cable reach or exceed 70 degrees at any point?
 
Ta - figured as much.

Almost there, just a query about lead installation from oven to wall FCU...
-2300W / 230v = 10Amps current expected through the electric oven lead at max.
-Understand that 2.5mm T&E does 24Amps circa (but not sure about unburied).
-Fuse in FCU would need to be 13Amps

If I have some spare 2.5mm T&E - this going to be okay for unburied oven lead to FCU?

Should I go for 4mm if unburied?

(BEKO manuals are flippin' useless and googlin is ambiguous).
2.5mm cable will be fine.
 
How are going to terminate this 2.5 cable from the FCU.
 
  • Like
Reactions: nicebutdim and DPG
Be interesting if it's coming out of the front flex outlet of an FCU !
 
  • Like
Reactions: nicebutdim
Hi, its all fitted a looks great. So thanks a lot for past advice(!)

Was a bit worried about the power wire on the back touching the oven when pushing it in.

But so far, no issues with it, or with any of the circuits tripping.
 

Attachments

  • IMG_20211224_201004.jpg
    IMG_20211224_201004.jpg
    90.5 KB · Views: 45
Did have another issue which someone on here may have an idea about?

The gas man who sealed off the connection said that was a small leak on the mains pipe that feeds the meter. He stuck some fairy liquid on it and there was a small bubble. I called Cadent who (after 4 hrs of messing around) changed the external pipping to the meter with some engineers during the evening.

The Cadent engineer then said there was a 2millibar drop showing and despite checking all the appliances with his sniffer (boiler, cut off gas seal for new oven, gas heaters, etc). cut off the gas on Christmas eve. I was horrified as there was no heating (even if the oven was working) on Crimbo day.

Does anyone know if they are allowed to cut the gas like this to a residential house when there has been no reported smell of gas, all appliances have been tested and the millibar drop on a tightness test is only showing 2millibar??
 
By the sounds of it they had to turn the gas off to repair something to do with the meter or the supply to it.

they will not be able to turn the gas to the property back on if there is a leak, unfortunately you are going to need the services of a gas safe registered plumber to find and repair the fault(s) within your house.
 
  • Like
Reactions: DPG
By the sounds of it they had to turn the gas off to repair something to do with the meter or the supply to it.
Yes, correct, in fact they used some balloon thing to stop the gas coming out before the shut out valve, so they could replace the shut of valve with a new one.
they will not be able to turn the gas to the property back on if there is a leak, unfortunately you are going to need the services of a gas safe registered plumber to find and repair the fault(s) within your house.
Apparently suppliers (British Gas) etc accept small leaks as long as there is no smell of gas (I think 8millibars depending on the meter in the house) - Cadent have permittable levels of a small gas leaks (as long as there is no smell of gas) as well, but in this instance they seem to have ignored their own operation procedures and just capped off all the gas to the house.

At the beginning the engineer kept blaming me by saying I reported a "smell of gas" which I did not (it was the fairy liquid around the shut of valve that alerted to the minor leak around the shut of valve) not any smell - and they could have listened to the call in to verify that. The shut of valve is high up in the garage and its so well ventilated it would have been impossible to smell any minor gas around that area in anycase.

I think its got something to do with them passing the buck to someone else to re-open the gas so they can escape any blame. Was a horrible thing to do at that time. Is there some recourse to this action if its not in line with their operating protocols?
 
Last edited:
I think a chat with a good independent gas fitter would be the best place to start.
they are going to be in a far better position to advise than a bunch of electricians.
 
  • Like
Reactions: DPG and nicebutdim
I think a chat with a good independent gas fitter would be the best place to start.
they are going to be in a far better position to advise than a bunch of electricians.
Got the gas turned back already by calling out an independent gas engineer (he was shocked by what they did as well).

Just was curious if anyone in this forum knew about the dark arts of Cadent. There was massive consequences to them cutting gas off on Christmas eve when there are elderly and vulnerable people in the house that could not stay at other people's houses due to Covid risks - and have no heating, no hob, no hot water. Terrible thing for them to do and think I should pursue it - so it does not happen to anyone else.
 
  • Agree
Reactions: James
I know Gas suppliers have more powers than The police in gaining entry to turn off gas in an emergency. So they can turn off your gas if it’s not deemed safe.

the supplier was correct not to turn on the gas until such time as the installationnwas deemed safe. They have a duty of care.

We electricians do not hav3 the power to turn off anyone’s electrics even if we think it’s dangerous.
However if we turn the power off to do some testing or a job and find the installation is unsafe, we cannot turn the power back on until such time as it is made safe.

so7nds like the same thing really, but it’s not.
 
  • Informative
Reactions: marconi
Got the gas turned back already by calling out an independent gas engineer (he was shocked by what they did as well).

Just was curious if anyone in this forum knew about the dark arts of Cadent. There was massive consequences to them cutting gas off on Christmas eve when there are elderly and vulnerable people in the house that could not stay at other people's houses due to Covid risks - and have no heating, no hob, no hot water. Terrible thing for them to do and think I should pursue it - so it does not happen to anyone else.

Difficult to say without knowing the full story, but imagine the headlines if they switched the supply back on when there was a leak, and something went wrong.
 
Terrible thing for them to do and think I should pursue it - so it does not happen to anyone else.

It would have been a terrible thing to put you and the household at risk. Pursuing this would be a waste of time as the engineers will be backed up all the way on this one.

He was protecting you and did what was in the best interests of anyone within the house.
 
  • Like
Reactions: nicebutdim and DPG
Difficult to say without knowing the full story, but imagine the headlines if they switched the supply back on when there was a leak, and something went wrong.
Like poor electrical connections😁😁
 
  • Funny
Reactions: nicebutdim
"Safe" is ambiguous, so there is an Operating manual which was ignored.
 

Attachments

  • 20220103 Cadent Operating Procedures.jpg
    20220103 Cadent Operating Procedures.jpg
    210.9 KB · Views: 56

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other

Thread Information

Title
Gas Cooker conked and electrical cooker replacement
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
109

Advert

Thread statistics

Created
advicewelcom,
Last reply from
westward10,
Replies
109
Views
16,824

Advert