Discuss 100 mA rcd on tt system? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
R
redrocket10000
HI, I've been asked to do a pir on a domestic installation, Means of earthing is a TT system using a 100 mA (not s-type) rcd as the main switch, covering all circuits. House is a rental property...Is there any real problem with this with regard to regs? would appreciate any advice thanks.
hmmm, could be a code 2 ( requires improvement ) or a code 4. really depends on how you look at it. if you, as the inspector, think there's potential risk then give it a code 2.
If there are socket-outlets that can reasonably be expected to be used for mobile equipment outdoors, I would go for a code 2.
Otherwise code 4 for general use socket-outlets, bathroom circuits and cables concealed in walls (if applicable).
think i would lean towards a code 2. recommend RCBO on socket outlets, if only on ground floor.
Reply to 100 mA rcd on tt system? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...