I have installed two rcd sockets in a plant room where I work I done this using 2.5 swa cable on a 16amp rcbo as there sockets will rearly be used the length is 15 m long is this ok
 
I disagree,
if there is a neutral to earth fault which device would trip?
unless there is a time lagging device like you have in a site MDU,
either the RCD or RCBO could trip and could result in a headache later
I would suggest that you downgrade the RCBO to an MCB.
The SWA has earthed armouring so an RCBO is not require

Richard
 
Last edited by a moderator:
I think the OP means the sockets are RCD protected by having used an RCBO. In which case all is well.
 
yes I understand that,
if there is a Neutral to Earth fault on the device that is plugged into the RCD socket then there are 2 Residual Current devices in series in the circuit.
As I stated before either of the RCD, or the RCBO could trip.
 
yes I understand that,
if there is a Neutral to Earth fault on the device that is plugged into the RCD socket then there are 2 Residual Current devices in series in the circuit.
As I stated before either of the RCD, or the RCBO could trip.

If my reading of the OP is correct then they aren't 'RCD sockets' - just normal sockets connected to an RCBO.
 
ok
I see what your saying.
if they are normal 13amp sockets being used as RCD sockets because they are protected by an RCBO,
yes I agree that would be ok

Sorry if I caused any confusion
 
I have read it about four times,it says to me,t he has run one swa 2.5mm fed from 1No 16amp rcbo, terminated to feed 2 No rcd sockets

Its a good enough confusing statement to compare with a lot of the regs
icon7.png
 
Doble - could you please enlighten us?!
 
Well Rockingit, at least we agree about somthing

I also don't disagree with you that if he HAS installed RCD sockets on an RCBO circuit then it's not a good solution!
 
Seeing as there's a lot of agreeing and dis agreeing going on
icon10.png


I will agree with dis agreeing, and disagree that I only agree just to dis agree
icon14.png
icon13.png
 
I thought it was just me that had been on the pop.......
 
Must admit, it reads to me that the socket-outlets are RCD type, and they are also protected by an RCBO.
Don't see the need for any RCD protection, unless the socket-outlets are to be used for mobile equipment outdoors?
 
Thats my thoughts Spin, are they for a specific purpose ? still no need for a RCBO and as it is plant room "skilled and instructed"?? as any one in there should either be trained, Skilled, and at least instructed,
Pict
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
16amp radial
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
Doble89,
Last reply from
the pict,
Replies
15
Views
2,996

Advert