Hi
I bought a holiday lodge last month and decided to test the circuits to see how they measured. The lodge itself is fed from a central point in the holiday village by a 16mm PVCSWA. The main earth wire terminates into a MET it looks to be a 10mm earth that is crimped onto the incoming earth, I cannot see what its crimped onto as the head the mains terminated into prevents this. Anyway I carried out the the normal tests on the circuits R1 R2 RN and these tested all within the expected parameters as an example the one of the rings measured R1.24 RN.24 R2 .39 and R1/R2 .25.
The other circuits all tested within expected parameters. The Ze measured .6, however when I powered up and did a Earth Fault loop impedance test the machine measured 23 ohms, this was repeated on all the sockets and the same measurement. Assistance required please as to the possible reason (s) for this.
Something not right
I would probably try checking the loop impedance at the outgoing side of the mcbs and try to narrow it down and recheck the resistance readings etc
you could have errors caused by RCD or MCB. worst i ever saw was a Ze of 0.2 but measured on the outgoing terminals of the rCD it was 341.
Something not right
Thanks for the response.
Yep I agree something is not right, when you say check the loop impedance at the outgoing side of the mcb what do you actually mean, I checked both ring circuits and cooker circuit and they read 23 ohms,
I haven't yet checked lighting circuits, but if 3 circuits read around the same then where now?
Could be the DB
You can check in a few spots, external, also where your socket wires connect into dB and along the final circuit
Ya your Ze and R1 and R2 are normal so
I'd be sticking a probe on the earth bar and checking fault loop at main switch ,rcds, mcbs on the outgoing sides
Did you disconnect anything at the met
May not turn out to be that at all either
I’ll go through it as you describe and I’ll let you know, as an aside I disconnected the main earth for the Ze test but reconnected it after. ?
I would put my bets on RCD uplift as @telectrix suggested, I had some BG ones a while ago that made some circuits wildly high Zs.
If you can do a bypassed Zs on the circuit that will prove it one way or another. To do this I isolate the supply then put a R1+R2 link cable in between live and earth at the furthest point on the circuit in question. Then put the tester on high loop and place between the outgoing circuit feed and the non isolated incoming live, this will give you a non uplifted reading to compare with your current one!
Be very careful when doing this test!
Thank you for replying, funny enough these are BG RCD's, If it is the RCD I can bypass it by feeding a spare MCB from the incoming feed block the neutrals from the mains
and then test the ring.
I would appreciate a sketch showing the process you describe , you can either email it to me or put it on here whatever is the easiest if you wouldn't mind.
Telectrix, thanks for reply, I appreciate it.
here is a method.you turn off the RCD and/or MCB. short L-E at point you want to measure. them MFT on hi current Zs setting (2 leads).bridge to RCD.MCB with the meter. this will give you a true Zs.
don't forget to remove the short before re-energising.
Good method, can't say I've ever had to carry this type of check in practice,don't even have a 2-wire tester
The theory is routine enough though
Is the high current reading like 20a ?
Better for troubleshooting those issues
something like that. the higher current helps to get past tarnished contacts, that's why low current test often gives slightly different results. ( well that's my theory, anyway ).
Yes that's my theory on the low current testing , should be more reliable at the higher current here
Similar to IR troubleshooting at 1000v where it can be more effective at locating a fault, when safe to test
Dont think you'll find these particular tests in any reference books will you ?
It is one factor, but even then wiggling the probes/clips on low Z systems usually gets a slightly lower value.
More fundamentally the bigger the test current the larger the delta-V, and so it is easier to measure that and reject the wobbles on the supply that are usually there. For example, if test current is 20A then 0.3 ohms Zs is going to show a 6V change - easy to spot on 230V.
But if the test current is only 15mA to avoid tripping a RCD then you are trying to see a 4.5mV change in 230V or 0.002% which is why MFT take a long time to switch it on/off over and over so the supply noise gets averaged out but the disturbance reinforced.
Hi
Do you know the earthing arrangement, you say you cannot see what the earth is attached too so could it be a TT earth and the rod has resistance of around 23ohms
I dunno just know the uk tns is 0.8 max ,.we.dont have it
Could that be like a submain at 0.6 external loop, 16mm pvcswa sounds like it
Guys, al
Hi There,
I measured the Ze and it was .6 so I would assume not a TT, I have asked the facility manager the question to confirm it.
I started again from the MET and retested Ze, that tested out at .2 ohms, don't ask me, I tested it numerous times and it didn't move from.6. The R1 & R2 values stayed the same as previously, I re-tested the Earth Fault Loop and it tested out .8 as I would have expected on one ring and 1.17 on the other, the cooker tested out at .11. I have no idea what happened here as there was no sign of the 23 ohms it tested out at when I posted the original plea for help.
Thanks to all for their inputs
No I didn’t, I have no explanation as to why this happened, it’s not the tester after the initial tests at the holiday lodge I tested my home address I knew the readings here and they tested as expected ??
Reply to Loop Impedance reading in the UK Electrical Forum area at ElectriciansForums.net
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...