thekingiam

Done a eicr on a tt no rcd protection and ze of 268 ohms.
3 Radials in 2.5mm going to 32 amp mcb.
Just been plastered throughout and some type of rewire i think, the house is going through a sale and was requested by buyers solicitor.
I was going to replace cu and put sockets on three seperate 20amp mcbs voltage drop not a problem as house is tiny.
Any problems cAn you see
 
Done a eicr on a tt no rcd protection and ze of 268 ohms.
3 Radials in 2.5mm going to 32 amp mcb.
Just been plastered throughout and some type of rewire i think, the house is going through a sale and was requested by buyers solicitor.
I was going to replace cu and put sockets on three seperate 20amp mcbs voltage drop not a problem as house is tiny.
Any problems cAn you see

A3 Radial 50m2 floor area, 20amp cb 2.5mm2 page 174 OSG
 
What about the 268 ohm Ra of the so called TT system earth, ....are you just intending to leave it at that existing value. Now what's the betting that the single electrode is a short thin twig that's of no use to man nor beast!! (except maybe as a test spike for an earth tester maybe!!) What's the Zs value with all bonding in place (if any)??
 
  • Like
Reactions: 1 person
Yeah read page 174 earlier, rod is stuck out of ground about 500mm so was going to wack it in and pee on it its on a main road though so i got to be carefull:pirate::pirate::pirate::pirate::pirate:
 
dok it in. replace with a decent screwed together sectioned rod. n't whac
 
Nothing wrong with a 20a radial

Ive never understood why loaded consumer units are always stocked with 16a mcbs rather than 20a
 
What about the 268 ohm Ra of the so called TT system earth, ....are you just intending to leave it at that existing value. Now what's the betting that the single electrode is a short thin twig that's of no use to man nor beast!! (except maybe as a test spike for an earth tester maybe!!) What's the Zs value with all bonding in place (if any)??

Funnily enough I've got 2 which I use for that exact purpose, test spikes for earth rod testing.

They also come out for small temporary generator jobs, when the ground is waterlogged and they're only running for 6hours max then they are fine
 
Yeah read page 174 earlier, rod is stuck out of ground about 500mm so was going to wack it in and pee on it its on a main road though so i got to be carefull:pirate::pirate::pirate::pirate::pirate:
500 mm? Lovely,simply tap in,25mm at a time,until Ra = 199,place garden gnome over projecting rod,retire for bourbons.:icon12:
 
  • Like
Reactions: 3 people
You'll probably discover that the reason it's 500mm proud is because there's a big rock under it!!!!
 
  • Like
Reactions: 2 people
that's why we have 40" masonry drills. alternatively, the drains may be under it. bang it in and keep it nice and wet.
 
  • Like
Reactions: 2 people
getting technical now. from big hammers to pme. :hammer:
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
20 amp mcbs on 2.5 radials
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
thekingiam,
Last reply from
Deleted member 9648,
Replies
14
Views
1,950

Advert