Hi

could someone please help me with a C&G question

when testing a TT earthing system for external earth fault loop impedence using a earth fault loop impedence tester

Why the earth fault loop reading can be recorded as the electrode value

Is it something to do with the resistance of the secondary winding , line conductor as well as the earthing conductor miniscule in comparison to the resistance of the general mass of earth

any help appreciated have my 302 exam and this is one of the questions that is niggling me of sample paper i have

cheers for any help with this
 
I don't know where 'windings' have come into it but think about the earth loop impedance path.

You're measuring the loop from a point using the live conductor through the whole loop including the earthing conductor(s) via the general mass of earth right back to the point you're testing at.

Therefore if the Ze reads OK without any parallel paths the chances are your earth electrode is ok.
 
The EFLI method should only be used as an alternative to the earth electrode resistance test (EERT) method when an earth electrode is used in conjunction with RCDs *, where the electrical impedance is relatively high (typically 10-200 Ohms) and precision is not required. Because the supply transformer secondary winding, line conductor and earthing conductor impedances are small relative to the impedance of the path through the general mass of the earth from the installation earth electrode to the supply earth electrode, the impedance reading taken can be treated as the earth electrode resistance.

* Most TT installations require RCD protection in order to meet the BS7671 maximum disconnection time.
 
Last edited by a moderator:

Reply to 2330 lv3 302 question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
663
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K
Hi all, I come in peace, I need help with an exam question. Q. A new circuit has been added to an existing three-phase installation forming part...
Replies
1
Views
1K
Hello, I took the opportunity over the lockdown to do 18th Ed course but theres a few bits im struggling with. Because its distance learning, the...
Replies
5
Views
1K
Hi. This is a gloriously messy installation I looked at this morning at a house a friend just purchased. It t became quickly clear it was more...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock