Discuss 2394 question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
L
LittleEd
Hi I am due to start the city and guilds 2394 course next month. I thought that I would have a look at some past questions to see what to expect. I am having trouble with one of the questions and was wondering if anyone could explain the theory to me.
16) The measured value of loop impedance for a circuit is 0.83Ω. If the temperature at the time of the test was 20C and the cable is 70C (factor 1.2) what is the corrected value. Ze = 0.4Ω
a) 0.43Ω
b) 0.86Ω.
c) 0.996Ω.
d) 0.916Ω.
I am using this formula to work out the question ZStest=1/1.20 x {Zs +Ze (F-1)}
I know the answer is 0.916 by cheating and looking at the answers, but i have no idea how they came to that answer. am I using the wrong formula and if i am where can i find the right on?
Thank you in advance
I would of said it was (c) 0.996.
The way I see it is the resistance of the copper changes by 2 % for every 5 degrees so the resistance will rise by 20 % if its temp rises to 70 degrees.
You have your measured loop impedance at 0.83 ohms at 20C and by multiplying by 1.2 (20 % )with give you the corrected value for 70 degrees .
IMO the resistance value at operating temp of 70 degrees would be 0.83 x 1.2 = 0.096 ohms.
I would have gone for the 0.996 as well.
The question practically gives you the answer they have given though.
Having a Ze of 0.4 leaves 0.43Ω as the resistance of the cable (sort of, and not how I would consider it)
0.43 *1.2 = 0.516
0.516 + 0.4 = 0.916
The factor given for the cable is 1.2 @ 70°C, if the cable is running at 70°C this does not mean that the supply from the substation is running at that level since the current carrying capacity is much greater on the supply than on a final circuit.
e.g. you have 16A circuit wired in 1.5mm² cable in conduit that is fully loaded then the cable should be close to 70°C, however the 100A supply is at less than 20% of its CCC and so would barely heat up.
However all this said, the general arrangement for temperature correction from 20°C to 70°C would be to multiply the resistance by 1.2.
I just want to say I really find Richard Burns to be a huge asset. I don't often see negativity from him and he is always very informative in his answers.
Here is a huge Thank you from me Richard.
You're only correcting your R1+R2 values and as such don't take in to account the external earth fault loop impedance.
Zs = 0.83
Ze = 0.40
Zs - Ze = R1+R2 (0.43)
R1+R2 (0.43) x 1.2 = 0.516
0.516 + 0.40 = 0.916
The answer is (d)
Thank you cprfenom.
LittleEd, I did forget to mention that the formula you were using is one to determine the maximum value of Zs (20°Ctest) permitted when you have the Ze and the tabulated maximum Zs from BS7671 (effectively converting the tabulated value from 70°C down to 20°C.
The actual formula you should have used (although the data is not really available in the question as it requires you to use the R1+R2 = Zs-Ze which is not accurate at all unless there is no bonding in place)
(rather than using the (divide by) 0.8 rule of thumb) would be:
Zs (70°C) = Ze +F(R1+R2test)
i always use this formulea Zs = Ze+ (( (r1+r2)*Ca))
M
Where Ca is the correction for ambient temperature and M is the multiplication factor. In this case !.2
I hope this has helped you and good luck.
Reply to 2394 question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Hi, I am currently studying to become an electrician and keep seeing this question (normally different values) and I am not sure how to work this...
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Hello, I took the opportunity over the lockdown to do 18th Ed course but theres a few bits im struggling with. Because its distance learning, the...
Hello everyone I'm Chris. I am taking the 2391 in February. This question is from the c&g main site under 2391 sample questions. Continuity of a...
4K