Discuss 3 core SWA supply with armour as N & CPC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

SparkTech

Hi All,

First thread in ages.

Recently went to a a pub to carry out some origin tests before they begin a total refurb.

It used to be a 3-PH supply / metering but they are only using 1-PH (red) with single PH metering.

I opened the service head to discover a core cable swa cable......

BUT they had used 2/3 of the armour as N and the rest of it earth-clamped with separate cable joining it to the Neutral.

So - on the outside it appeared to be TN-S but they made it a Temp TNCS.

N-CPC voltage at a DB near the supply intake indicating 230V!

Are DNO allowed to do this??

Customer advised that they had applied for a 3-PH supply, they only have 3 cores so I assume a new supply cable will have to be run TP&N and armour as CPC.

Any thoughts . comments appreciated.

Regards
 
Hello, it was defo a swa cable and not a split consentric cable?? could look similar but are different.

(don't want to sound patronising but recently used some split con cable myself and tought then how similar it looked to swa)

Ross.
 

Reply to 3 core SWA supply with armour as N & CPC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

If cpc core is present i.e. it's either 5 core three phase or 3 core single phase — is a banjo connected with a brass screw into steel trunking...
Replies
7
Views
1K
Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table...
Replies
13
Views
1K
I have a strip light in the kitchen operated from a single switch. I want to replace it with a straight bar 4 spot array. There are three supply...
Replies
2
Views
445
I was the 2nd sparks taking over a garden office supply job. The first sparks had fitted 10 sq mm 3 core SWA, but it actually had brown, blue and...
Replies
5
Views
804
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock