I am installing a 6mm armoured cable to supply a detached garage with a 2-way DB with 30mA protection. the supply cable is NOT buried but goes overhead on a suspended wire. my? is does the supply cable need rcd protecting? if so do i need to discriminate some how or will it be100mA?:confused:

this is a domestic installation.
 
Last edited:
Do you have RCD protection at the main db? If so why not put the whole installation on the RCD side and use a main switch in the garage board!;)
 
there is no rcd protection at main but the client doesnt want to walk back to the mains if something trips. he just wants to reset it in the garage.
 
The sub main does not require RCD protection, as long as its swa, if the sub CU has an RCD main switch or RCBO's on each circuit.
 
The submain does not have to be rcd protected because it has earthed armouring but I think that you cannot extend the pme out to the garage you will need to install a earth rod so is a seperate system.
 
The submain does not have to be rcd protected because it has earthed armouring but I think that you cannot extend the pme out to the garage you will need to install a earth rod so is a seperate system.


True, but only if theres
Extraneous conductive parts in the detached building, (gas, water supplys ..etc..Otherwise its not needed
 

Reply to 30mA rcd protesction? in the Australia area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
724
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
546
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock