whats the material?...
factor of K for copper is 115...so
assuming its this we go:
lets say the current needed to acheave a disconnection time of 5s was 160A we can go:
160*X5=128000.....we then apply the square root to this so:
128000 square root=357,7708764...now we divide this by our factor of K (which in the case of copper is 115)...so:
357.7708764/115=3.11 (to 2 decimal places)....this would be the min. CSA required