I don’t see a problem with that, as long as it’s suitably sized; indeed I did suggest something similar earlier. The only issue I would have, is that this cable is connected to the fixed wiring with a suitable JB with suitable strain relief, and where it exits the split conduit, a suitable grommet is used.

BS7671 reg 521.9.1 (I think) mention use of flexible cable used in fixed wiring. Only caveat is using heavy duty flex. But in your case I can not see it be subject to any mechanical damage.
 

Pete999

-
Esteemed
Arms
Reaction score
16,657
I don’t see a problem with that, as long as it’s suitably sized; indeed I did suggest something similar earlier. The only issue I would have, is that this cable is connected to the fixed wiring with a suitable JB with suitable strain relief, and where it exits the split conduit, a suitable grommet is used.

BS7671 reg 521.9.1 (I think) mention use of flexible cable used in fixed wiring. Only caveat is using heavy duty flex. But in your case I can not see it be subject to any mechanical damage.
Good thought Mate, I think the answer is to string the So called Electrician up that Decided to strip the Mech Protection from the cables and thread them down a conduit,and chuck his tools away, do every one a favour and rid the world of these cowboys and stop them poncing on the unsuspecting general public, and hear was I thinking that only suspect car dealers were up to this malarkey.
 
Reaction score
9
So I am still waiting for the electrician to come back, I have heard from him & have not gotten a date from him on when he will return.

I do have another question regarding the grouping factor that will be applied to the three cables he has installed in the conduit. The cables/circuits & MCB's are as follows :

4mm2 T&E - 32 amp MCB

2.5mm2 T&E - 20 amp MCB

1.0mm2 T&E - 6 amp MCB

Am I correct in saying that because the conduit contains three circuits the grouping correction factor would be 0.70?

Then I am totally lost on how to apply this correction factor to these these circuits.
 

Pete999

-
Esteemed
Arms
Reaction score
16,657
Is this a continuous solid conduit system, or an oval conduit for burying in the wall the use of twin and earth suggests the later, can you confirm please?
 

Mike Johnson

-
Esteemed
Arms
Reaction score
1,360
That must be a very large conduit to accommodate those three cables and keep within the requirements of BS 7671 and not exceed 45% of the net cross-sectional area.
 
Reaction score
9
Is this a continuous solid conduit system, or an oval conduit for burying in the wall the use of twin and earth suggests the later, can you confirm please?

That must be a very large conduit to accommodate those three cables and keep within the requirements of BS 7671 and not exceed 45% of the net cross-sectional area.

He has used 25mm black conduit that is round, it is on the exterior wall of the house.
 

Mike Johnson

-
Esteemed
Arms
Reaction score
1,360
Ok I will bite, 25mm dia conduit has an internal area of 78.5mm sq, 4mm T&E has a nominal dia of 37mm sq so even without the 2.5 & 1 T&E the 45% space requirement is not maintained.
 

Mike Johnson

-
Esteemed
Arms
Reaction score
1,360
Sorry should have said "with the 2.5 and 1 the 45% space etc:

2.5mm T&E being 32mm sq and 1mm T&E being 24mm sq.
 
Reaction score
9
So in layman's terms there are to many cables for that size of conduit?

If the 4.0mm2 cable was removed would that compile with the regulations?

I presume this regulation is to prevent the cables from over heating?
 

James

-
Mentor
Esteemed
Arms
Supporter
Patron
Reaction score
3,364
So in layman's terms there are to many cables for that size of conduit?

If the 4.0mm2 cable was removed would that compile with the regulations?

I presume this regulation is to prevent the cables from over heating?
Also,to allow cables to be rawn in without damaging them
 

Mike Johnson

-
Esteemed
Arms
Reaction score
1,360
The cross section of T&E is a bit strange, as the cable is deemed to be the diameter of its major axis when in reality its anything but, so most electricians use a bit of common sense where this is concerned.
 

Reply to Advice On Rewire Of Lighting Circuit in the Electrical Forum area at ElectriciansForums.net