Discuss Anyone much experience with Relays? in the Canada area at ElectriciansForums.net

Reaction score
7
I'm embarrassed to say I know very little about Relays.
Never really had much dealings with them.
I have a job next week and from the email I got from the company I will have to do the following:

1: Install new speed drives in new enclosure with MCBs ( Either 1 or 2 Drives )

2: Mount new Panel on AHU

3: Either pull back Motor cables or install new cable if necessary from motors into new panel ( either1 or 2 motors depending on Unit ) max run approx 10m

4: Run new mains cable from existing panel to power drive panel ( Max run approx. 10m)

5: Connect mains and motor cables

6: Remove existing contactors and install relays for new control.

7: Relays powered by existing contactor supplies.


8: Aux controls through contactors now across new relays.

9: Enable and fault control via .75 multicore cable run from new relays to drives.

10: Test and commission drives and AHU unit operation

The bits in Bold are the ones I am having issue's with,I have never done this so am a bit worried how it will work out.
This is a big contract for me as there will be 45 of these jobs to be done,all exactly the same in different buildings across Ireland,so I want to be sure I have it right from the start.
Any advice would be great.
 
Last edited:
I'm embarrassed to say I know very little about Relays.
Never really had much dealings with them.
I have a job next week and from the email I got from the company I will have to do the following:

1: Install new speed drives in new enclosure with MCBs ( Either 1 or 2 Drives )

2: Mount new Panel on AHU

3: Either pull back Motor cables or install new cable if necessary from motors into new panel ( either1 or 2 motors depending on Unit ) max run approx 10m

4: Run new mains cable from existing panel to power drive panel ( Max run approx. 10m)

5: Connect mains and motor cables

6: Remove existing contactors and install relays for new control.

7: Relays powered by existing contactor supplies.


8: Aux controls through contactors now across new relays.

9: Enable and fault control via .75 multicore cable run from new relays to drives.

10: Test and commission drives and AHU unit operation

The bits in Bold are the ones I am having issue's with,I have never done this so am a bit worried how it will work out.
This is a big contract for me as there will be 45 of these jobs to be done,all exactly the same in different buildings across Ireland,so I want to be sure I have it right from the start.
Any advice would be great.

remove the contactors but identify and retain the wires connected to A1/A2. the contactors will have Auv contacts, these will be labelled Normally Open or Normally Closed, identify and retain these in their respective pairs. depending on the drive it may have an onboard powersupply (24VDC). take this supply to a N/O contact(likly) on the relay and from here back to the drive enable/run terminal. most drives have a fault internal relay. you may want to routue your A1 wire through that so if the drive develops a fault it will drop out your main relay.
this is a general description as i dont know drive manufacturer etc
hope this helps
perhaps this is stating the obvious but your contactor A1/A2 connects to your relay A1/A2 and match your AuX contacts to N/o or N/C on your relay
 
Last edited by a moderator:
6: Remove existing contactors and install relays for new control. The contactors previously was the DOL starter, I'm assuming, so what used to switch in the DOL will now signal to the inverter(s) in the form of a relay. The contactor is basically a robust switching relay. Again this will become the inverter run relay.

7: Relays powered by existing contactor supplies. As stated above, the relay will be signalled in the same way as the contactor.


8: Aux controls through contactors now across new relays. The relay contacts will now take the place of the contactor contacts as in switching normally open / closed as required.

9: Enable and fault control via .75 multicore cable run from new relays to drives. So using 0.75mm2 cable the relay will switch a normally open contact to signal the inverter(s) to run by utilising the inverter's onboard control PCB ie. P24 to RUN of Mitsubishi inverters and PLC and PLC to FWD of IMO Jaguar inverters.

Inverters have a fault alarm contact within there control PCB, some can be configured within the inverter parameters to switch on fault, switch when inverter ready, etc... so you may have to configure this to your needs.

Should the DOL have had an overload fitted, the wires from terms 95 & 96 can be taken through the inverter alarm contact. Also, you are best to have an auxiliary contact fitted to the mcb indicating its status, plus have a local isolator fitted close to the motor if the control panel is out of view, fitted with an auxiliary contact (pref early make/break) so the inverter does not run when the isol is off.

Finally confirm that the emergency stop and safety circuit is correct for the type of system... and all regs, etc... satisfied.

Good luck.
If you want any circuit dwgs to clarify, please let me know.

.
 
MS Word.

I've removed some info and logos from the title bar at the bottom.

Takes a little practice and some experimenting but looks professional without the cost of CAD.
I'm certified in AutoCAD but find Word is always to hand, accessible and easy to use.

I then transfer it to .pdf so it's not too easy to copy and use in Word as a template. I'm sure it can in the right hands with shareware off the t'interweb. ;)

Regards
s.f
 
Last edited by a moderator:
MS Word.

I've removed some info and logos from the title bar at the bottom.

Takes a little practice and some experimenting but looks professional without the cost of CAD.
I'm certified in AutoCAD but find Word is always to hand, accessible and easy to use.

I then transfer it to .pdf so it's not too easy to copy and use in Word as a template. I'm sure it can in the right hands with shareware off the t'interweb. ;)

Regards
s.f

i,m impressed, not used autocad since 2005 so wouldnt no where to start, rececntly looked at the main screen for autocad electrical 2009 and just felt sick.
been trying to get to grips with microsoft visio but find it frustrating having to fragment/make/save your own symbols,
think ill give word a go as i use it most anyway
cheers
 
Can I have a beer please silver bar man ! pack man

Hmmmm... I work in ahu controls and each one is so not the same. I find removing the links, belling them out and start again is the best bet, as with a rewire of a control panel can start a lot of problems.

What is the control set up ?
What software ?
How do you propose to commission the ahu ?
Heater batts need the fan to run on after they stop or you can get a fire. Is timeclocks in the panel ?
DPS set up ?
Outside air ?
Inverters ?

Lots to think about, as you cant just change contactors for relays with a rewire.
 
Can I have a beer please silver bar man ! pack man

yes.jpg


Yee know too match

;)
 

Reply to Anyone much experience with Relays? in the Canada area at ElectriciansForums.net

Similar Threads

Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
583
Hi Everyone, New to the forum but hoping I can find a little help with my restoration project... I am adding a secondary wiring "system" to my...
Replies
14
Views
888
Hi all I am new to this forum and hope this is right placed and of interest. I would like to make a setup with one or more impulse relays...
Replies
9
Views
1K
Mileage: 112223 - DTCs - P0480 cooling fan. Also codes in TIPM P0691, P0692 for cooling fan control circuit. Tests/Procedures Performed: 1...
Replies
0
Views
581
I have a loading arm on a vehicle powered by a hydraulic motor powered by a 12 volt motor. The motor is initiated by proximity switches on the...
Replies
0
Views
760

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock