I have been asked by my company to audit random EICR,s from our contractors .
This is to consist of reviewing the report and an hour on the site (tenant occupied).
so far i have thought to conduct a ZE (Zdb) ring testing,RCD, and random ZS on some circuits.
im not sure IR would be fair as i wont have time to disconnect everything.

does anybody have any ideas or opinions on how to test and compare while making it fair but to stop any possible drive by types?
 
Ze and a some random Zs testing will give you a fair idea of the validity of the original Eicr

r1 r2 rn on the rings will also be interesting to compare
 
This is something I did a lot!

Tbh most of the time I didn't even go to site, just like many of the examples we see raised on this forum, just looking at the documentation shows it's complete rubbish. The most egregious is the sort of "c1 fusebox in plastic, must be replaced £5k to fix" type thing.

When I did go to site to check (paperwork is OK, but have my suspicions) then most of the time it would be visual which almost always is sufficient to identify the invalidity of the report.

Occasionally, yes I would actually get a screwdriver or even a tester out to check things, but in these cases the actual tests would be specific to the concerns I have with the report (eg a rfc where the R1+R2 does not follow from the r1+r2 values, or circuits with unusually high or low values)

Only a couple of times did I actually do what might be called a full examination, which in each case I did everything! - these being used in court to demonstrate just how poorly/fraudulent the so called reports were.

It really depends on what you are being asked to do, in my case most of the time it was a sanity check on the codes applied (is red/black cables really a c1? Etc) [OK may be a bit of an exaggeration], in others just to confirm if the supplier is doing a proper job.

In both these cases it is usually very easy to see it is wrong, at which point once you can Identify/demonstrate its clearly wrong, it's not worth continuing, unless of course you are going to follow a legal course of action
 
As above... in many cases the paperwork is the giveaway . Its all copied and pasted . Then normally within 20 mins and a few questions to the tenant .Its obvious if it was a "drive by " EICR .
 
If you get 10 EICR by the same person on the same date you know something is wrong. As to testing even between different MFT I have had there are variances at sub 1 ohm that while complying amount to diddlysquat in accuracy terms as parts of an ohm measured with an MFT is just variable by type of MFT alone. I wonder what happened to the QS then, asleep on the job? If you find something inconsistent then you investigate further just like EICR really.
 
Last edited:
As above start with a good look at the paperwork and talk to the tenant.
A lot of dodgy reports can be spotted from just the paperwork, and finding out how long they were there and if they even turned the power off will give some clues.

If any test results on the report look suspicious then they are the ones to check.
 

Reply to Audit of EICR’s from contractors in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
Afternoon all. Bear with me on this one... Despite having been involved in the electrical industry for many years, I'm only just about to embark...
Replies
15
Views
2K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
969

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock