Can anyone tell me if it is legitimate to install cables into a chase in a lath & plaster ceiling and then plaster over? The reason I'm asking is because I have been asked to quote for replacement of a vermin damaged lighting circuit which is above a lath & plaster ceiling and there is no access to it from above and the customer would like the cable protected from any possible future vermin damage.

BTW I just asked NICEIC tech help and was told I couldn't unless it was provided with mechanical protection as it's less than 50mm above the ceiling which I can see the point of if it was running through a joist but it isn't.

Cheers
 
The NICEIC are correct, it needs to be >50mm or mechanical protected.
Or kept on the surface.
Or you could run swa.

Or how about running micc?
 
Last edited:
bs7671 aside. damage to the structural integrity of the ceiling precludes this method.
 
Can anyone tell me if it is legitimate to install cables into a chase in a lath & plaster ceiling and then plaster over? The reason I'm asking is because I have been asked to quote for replacement of a vermin damaged lighting circuit which is above a lath & plaster ceiling and there is no access to it from above and the customer would like the cable protected from any possible future vermin damage.

BTW I just asked NICEIC tech help and was told I couldn't unless it was provided with mechanical protection as it's less than 50mm above the ceiling which I can see the point of if it was running through a joist but it isn't.

Cheers
Could you not use a fire tuff type cable BS8436 which would comply with Reg 522.6.204
 
Firstly the NIC are wrong again as you can replace cable, as long as it takes the same route and had the same CSA without applying futher protection.

as for the fauna that is the issue, you need to protect the cable from it as if it has happened once it will more than likely happen again in the future.
 
Firstly the NIC are wrong again as you can replace cable, as long as it takes the same route and had the same CSA without applying futher protection.

as for the fauna that is the issue, you need to protect the cable from it as if it has happened once it will more than likely happen again in the future.

They're not wrong Diillb, The op is replacing a cable that is above the existing ceiling, not one that is already in the plaster.
He asked them 'if it is legitimate to install cables into a chase in a lath & plaster ceiling and then plaster over? '
Would you really tell him that's ok and complies with the regs?

Your second point is a good point though.
 
A slight misunderstanding on my part, but I dont know how the OP is going to chase put thelaster wothout potentiailly damaging the lats.
 
micc surface, polished to a high sheen. make a feature of it.
 
Can anyone tell me if it is legitimate to install cables into a chase in a lath & plaster ceiling and then plaster over? The reason I'm asking is because I have been asked to quote for replacement of a vermin damaged lighting circuit which is above a lath & plaster ceiling and there is no access to it from above and the customer would like the cable protected from any possible future vermin damage.

BTW I just asked NICEIC tech help and was told I couldn't unless it was provided with mechanical protection as it's less than 50mm above the ceiling which I can see the point of if it was running through a joist but it isn't.

Cheers

If it is not running through joist's, why can't you pull through on existing cable.?
 

Reply to Cables in ceiling in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi There Just a quick one, I'm wondering what's everyone's thoughts on this are. A subby has clipped a cable to a plaster board ceiling using 3m...
Replies
8
Views
704
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
799
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
574
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
289
I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
492

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock