Hi all....for fixed wiring testing, does the test equipment (Fluke and Megger in this case) have to have a calibration certificate from an independant organization. i.e we cant calibrate it and certify it ourselves?
Do you have calibration equipment that can fully test every function and range of the MFT?
Thanks...and does the calibrtion of the calibration equipment need to be done independantly?
The calibration process/results need to traceable to national standards somehow, so if it was done by an 'independent' company (that's fine) you would expect them to be accredited by UKAS (assuming UK) for calibrating that particular type of equipment, e.g:
(I'm not saying your company needs this accreditation, but normally the people who calibrate calibrators need/have it!)
If you bought the necessary calibration equipment, you would need a procedure for the calibration, records of competence and training for the staff carrying out the calibration, periodic calibration of the calibration equipment you have bought (which is much more expensive than the fluke/megger etc calibrations), and to keep records of the results and any adjustments to the equipment to put it back into spec, all of which should be overseen by some sort of management/quality assurace process in the company.
It does depend on the complexity of the equipment, but my experience is that it is more costly for a small to medium size business to try to do calibration in-house, than it is to sub-contract calibration of test equipment to an accredited calibration house.
I’d say not as long as the calibration equipment your using to test the calibration equipment is also calibrated by whoever has equipment to calibrate that is also calibrated.
Can you actually buy fully calibrated calibration equipment ? Wouldn't it have to be calibrated by someone first before you calibrate it to test your equipment ?
It should come from the manufacturers with a full calibration certificate (except sometimes you have to ask for it and/or there is an extra charge!), and then it needs to be re-calibrated periodically (period usually specified by the manufacturer of the calibrator/ may depend on useage), say annually.
And then over a period, if every time the calibrator is sent away for calibration you ask for pre-cal check results, if it's always within calibration before it's calibrated (hope you are following!), you can decide on the evidemce to extend the calibration to say two years etc etc.
But these processes do need to be technically valid, systematic, and with all the records kept, to hold up to any investigations heaven forbid.
Here's just the thing (if you can find the missing parts, fix it, and pay to have it calibrated!)
And then buy the test gear to calibrate the RCD testing part of the MFT.
Reply to Calibration Regulations in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
Hi all My Fluke tester failed on one test today while having it's annual calibration, the continuity resistance test current. Test Current -...
Hi I purchased my Megger X1 in July last year so only 7 months old, having been a Megger fan for 20 Years... I've now had the opportunity to get...
Hi, So I have decided to sell my Megger MFT1721 - See photos below. Originally I bought this for when I was doing my C&G 2391-52 course & then I...
Just thinking about selling MFT's and single test equipment. The idea being I buy stuff from Ebay and sell it on ebay, which I am doing at the...
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...